Recent content by flexyboy

  1. F

    Ideal Logic Heat 12 boiler fault

    Still no reply from ideal tech, obviously a bit complicated for them. No other input from anyone ?? as my original post of fault still stands
  2. F

    Ideal Logic Heat 12 boiler fault

    Johntheo5 I have checked SL ( with a DMM and digital scope) and its stable at 240v when it should be but i take your point of adding an additional load to verify. thanks
  3. F

    Ideal Logic Heat 12 boiler fault

    I take your point re the s plan although there are 100k's (or more) of y plan systems operating perfectly ( apart from the slight issue of the valve motor continually using power under certain conditions) I note that you did not mention the pump so i assumne you do not believe that would...
  4. F

    Ideal Logic Heat 12 boiler fault

    existing pump is a Grundfos UPS 15-50 N 130 set at No.3 flow rate
  5. F

    Ideal Logic Heat 12 boiler fault

    double checked (infact about quadzillion checked !!) wiring in JBox for connections to mid pos, valves and room and tank stats, to boiler. all as per spec. It seems to come back to flow when just CH selected, even though pump is powered and running aven though allm rads getting hot ? nd system...
  6. F

    Ideal Logic Heat 12 boiler fault

    Hi again, sorry for delay in posting, away dilalio with 3 port manually opened (to mid point presumably) and just CH selected, boilere beahves as above. That is c on boiler and SL at 240v and pump at 240v and running. blue burner light on for a few secs and then off.. (de selectmanual overide...
  7. F

    Ideal Logic Heat 12 boiler fault

    I have not tried that combination. I will do that later on today and repost. Special thanks to dilalio and madrab for all their useful and knowleable input so far
  8. F

    Ideal Logic Heat 12 boiler fault

    confirmed by a c on display panel
  9. F

    Ideal Logic Heat 12 boiler fault

    Yes SL on boiler strip
  10. F

    Ideal Logic Heat 12 boiler fault

    yes, tested with DMM, constant 240
  11. F

    Ideal Logic Heat 12 boiler fault

    But all rads are getting hot, suggesting that circ pump is ok, and spindle spins freely. Not sure on pump age the boiler is shutting down within couple of secs. Not even ideal can get a boiler to raise temp that quickly !
  12. F

    Ideal Logic Heat 12 boiler fault

    removed cyl stat which is a basic mechanical 3 contact type. common, norm closed and norm open, this all fine when tested
  13. F

    Ideal Logic Heat 12 boiler fault

    Madrab As in my or post, all rads get hot when CH and DHW selected sytem DOES shut down when cylinder stat satisfied
  14. F

    Ideal Logic Heat 12 boiler fault

    existing system, new build from 12 years ago. As per original installation. There is no mag filter madrab - I totally agree something not right. I cannot get my head around there being a call ( c ) on boiler display whether on HW only or CH, and the boiler somehow differentiating c for CH only...