    It will almost definatley be the pin scaled/siezed on the water valve have changed loads of these on vaillant vcw`s
  2. G

    pressure keeps going to 3 bar worcester924 elec

    filling loop letting by or faulty expansion vessel
  3. G

    GLOW WORM, NO HOT WATER

    hot water heat exchangers gone mate..........
  4. G

    flame rectification problem

    got a baxi inset super 3 ks gas fire it lights pilot flame ok but carries on igniting and will not go to main flame??? any ideas???? oxy pilot has been replaced & p.c.b
  5. G

    Potterton Netaheat Profile boiler tripping

    sounds like a dodgy overheat thermostat to me mate... sometimes through age the contacts get weak and trip out intermittantly. replace o/h stat
  6. G

    Header tank overflowing

    Sorry I don`t understand what u are trying to say??? The system is: gravity hot water 2 x 28mm pipes one is flow to the cylinder with vent pipe to F&E tank one is return to the boiler with cold feed from F&E tank. pumped heating 2 x pipes for heating 22mm flow with double check...
  7. G

    Header tank overflowing

    nope i changed the pump myself 2 years ago its pumping back into the boiler (return pipe) thanks for that though any more suggestions??? this ones really giving me a headache!!!!
  8. G

    Replaced Pump - boiler still slapping and banging

    system doesnt look piped up correctly to me!!! where is the boiler in your first photograph??? where does that 22mm pipe go coming off the left hand side of the air seperator (copper cup thing)
  9. G

    Replaced Pump - boiler still slapping and banging

    The PROPER way to set up your system bypass is to use a temperature gauge and slowly adjust the gate valve accordingly until you get a 11@c temerature differential between flow and return (on the bypass circuit)
  10. G

    Header tank overflowing

    Wondering if anyone can suggest why and offer a solution...... I have been working on a baxi back boiler, gravity hot water, pumped central heating. Everytime you turn the c.heating on the tank is filling up from the cold feed connection raising the water level in the F&E tank and then pushing...
  11. G

    Potterton Puma 80 Hot Water is going HOT/COLD

    It sounds to me that you may have a partially blocked hot water heat exchanger, which requires de-scaling or more than likely replacing. Either that or its a faulty D.H.W temperature sensor. Either way you require a heating engineer to determine the fault and rectify the problem.
  12. G

    Help !!! low water pressure light on, no CH.

    obviously you wouldnt leave a "dangly live end"!! you would use electrical insulation tape and tape it up, the wire is in a insulated spade connection anyway and unlikely to cause a problem. Firstly Remember this is only a temporary measure to get heating tonight. And secondly i would not...
  13. G

    Help !!! low water pressure light on, no CH.

    Common fault on potterton puma/combi 80, the problem is the actual low water pressure switch, this is located behind the printed circuit board screwed into the diverter valve. The easiest instant cure is to remove one of the 2 wires going to the switch. the long term cure is to drain the...