Recent content by Johntheo5

  1. J

    New build hot water issue

    Almost like trying to get blood out of a stone.
  2. J

    Grundfos UPS 15-50 pump intermittently trips MCB/RCD – repair or replacement?

    Its the best hydraulic efficiency on the CC3 curve, not sure why its shown, you can see it in the calcs if you do the exercise at 3.5M & 1.8ms/hr. The overall efficiency is 42.09% so a hydraulic efficiency of 69.2% means a electrcal (motor) efficiency of ~ 42.09/69.23 (x 100), 60.08%, there are...
  3. J

    Grundfos UPS 15-50 pump intermittently trips MCB/RCD – repair or replacement?

    No the efficiency for both is the same in the examples I gave in posts #14&16, the hydraulic power required, is, (using my calc) (MXLPM)/6.14, so (3X16.666)/6.14, 8.143W, actual power ~ 21W, Effic=8.143/21, 38.78% Its difficult to give a fair comparison for the UPS2 vs the 6M Wilo as the UPS2...
  4. J

    Grundfos UPS 15-50 pump intermittently trips MCB/RCD – repair or replacement?

    They all have the same/very similar efficiencies, the UPS3, above, on CP1 at 3.0M & 1ms/hr (16.7LPM) flow consumes 22W, my Wilo Yonos Pico 6M would consume 21W. Unfortunately, the UPS3 (& UPS2) do not display the power consumption, most, now, display the flow and the power consumption.
  5. J

    Grundfos UPS 15-50 pump intermittently trips MCB/RCD – repair or replacement?

    The UPS3 is a giant of a pump, 60W vs ~ 35/45W for other 6M pumps, also, its constant curves are, in effect, constant pressure curves so will still maintain a 6.2M head at over 19LPM but changing to CC1 will give a more reasonable setting at 4.2M or CP2 will maintain 3.0M, so not really the...
  6. J

    Grundfos UPS 15-50 pump intermittently trips MCB/RCD – repair or replacement?

    For anyone with a OV system, if installing a new circ pump, its well worth taking a photo or noting the original pump details and mode/settings as some systems are quite sensitive and can suffer from pump over/air ingress. I have seen more than one reference to the UPS3 which is supplied in...
  7. J

    Grundfos UPS 15-50 pump intermittently trips MCB/RCD – repair or replacement?

    No issues in replacing with either as long as the external dimensions are the same. Before purchasing the 5M Yonos Pico, have a look at the Selectric's speed setting, if its on speed 3, a 6M Yonos Pico might be more suitable, how many rads have you got?.
  8. J

    Electric shower only produces scolding hot or ice cold in hotter months. Any idea what I can do to fix this or is this normal?

    Eco power setting on most showers is generally ~ 60% of full power so yours certainly shouldn't be greater than say 5.0kW. At a present mains temp of 17C it only requires a flowrate of 3.12LPM to have a comfortable 40C shower, if it's just about reaching its cut out temperature of 50C, but...
  9. J

    Is this horizontal Tank Installation correct?

    A air pocket will build up in the "top" of the UVC when installed as shown. At the stated 40 deg rotation away from the vertical means the immersion elements and the stat rods/pockets are pointing upwards at a angle of 50 deg. Using a few assumed dimensions, ie cylinder dia of 560mm and...
  10. J

    Is this horizontal Tank Installation correct?

    While probably not related to this water hammer problem I wonder would it help if the cylinder was drained down and refilled with a HW tap opened.
  11. J

    Is this horizontal Tank Installation correct?

    That very strange orientation will probably affect the immersion/stats as the elements are designed to be horizontal, since you are familiar with electrics it should be very easy to check with a multimeter if/when the stats are switching, even turning them up/down should result in a audible...
  12. J

    Is this horizontal Tank Installation correct?

    Thanks, also take a photo of the details on the UVC itself under "Product Data"
  13. J

    Is this horizontal Tank Installation correct?

    Can you show exactly where the expansion vessel (Lower right??) is piped from, also the writing on the labels on all the devices on the cylinder eg. pressure reducing valve, expansion relief valve, and the temperature and relief valve (T&PRV) on the cylinder itself. Also, the vol (capacity of...
  14. J

    Water hammer from unvented cylinder

    Have you tried any mods over the weekend to address the problem??
  15. J

    Water hammer from unvented cylinder

    Just to recap. Original install: Only one (ICG) PRV, cold taken off the balanced ICG port, but EV take off from a T downstream of the ICG and not from the port on the ICG. Don't know if the system worked OK for 6 months or so? before water hammer, but a PRV was/is installed upstream of the ICG...