Recent content by Johntheo5

  1. J

    Water hammer

    What capacity EV (arrestor) and precharge pressure??
  2. J

    Viessmann Weather Compensation

    I think a "normal" on/off roomstat will still just switch off the boiler if the roomtemp exceeds the stats setpoint temperature, if you want WC only, just set the roomstat higher so that it will not switch off the boiler. My OT often drops by 5/7C overnight but my roomtemp by less than 2C (with...
  3. J

    Gone through multiple Mira Thermal Switches

    That 20 minute behaviour certainly doesn't indicate that the elements stayed energised after switching off the shower. The heating can including the two elements contain 0.23L of water (I measured it years ago on a similar 9kW scrapped shower) so this 0.23L will be totally evaporated in less...
  4. J

    Gone through multiple Mira Thermal Switches

    Present (mine) mains temp is 12C, a showering temp of 40C (assuming a 9.0kW shower) requires a flowrate of 4.61LPM, if the showering temp reaches 48C (TCO, auto reset trip), then the flowrate must fall to 3.58LPM, if the showering temp reaches 72C (TCO final and no reset trip) the flowrate must...
  5. J

    Water hammer

    Try that then, why not.
  6. J

    Water hammer

    Yes, I would try that, it won't cost the earth.
  7. J

    Water hammer

    Looks like there may be another NRV just before the PG. Just open the outdoor tap and the kitchen tap fully but slowly and note the pressure, it should fall, even if only by a small amount, then shut both taps very slowly and ensure the pressure returns to normal. I would install a 2L EV...
  8. J

    Horstmann Electronic 7 not supplying 240v

    Ensure measurement is between live(s) and earth first and then lives to neutral.
  9. J

    Air in system - Update

    Don't know if your gas? boiler had/has a external circ pump and if it had been renewed with a Grundfos UPS3 at any stage previous to the air problem, the UPS3 is dispatched set to its highest setting of 6.4M, not only that but this very powerful pump will circulate over 18LPM and still almost...
  10. J

    Gone through multiple Mira Thermal Switches

    Strangely enough, or maybe not, I had a 9.0kW Mira Sport for ~ 18 years, now replaced with a 9kW Triton T80Z, due to ongoing external waterworks the mains pressure was frequently quite low or non existant for hours each day so I installed a lever valve (with a DCV at the mains), to use the...
  11. J

    Gone through multiple Mira Thermal Switches

    The TCO contains two sets of contacts, wired in series, one set of contacts open when/if the water temperature reaches 48C and is self resetting, the other is set to around 72C, if that opens then the TCO must be renewed, (and fault found). the 48C set can be heard operating every time you...
  12. J

    Water hammer

    Not sure what you mean by the above, its the air end pressure you are checking and setting so losing the water side pressure is correct and the only proper way to check it, what pressure have you set it to with the water side disconnected?.
  13. J

    Water hammer

    Off the mains may work.
  14. J

    Water hammer

    I honestly didn't think cleaning the strainer would do the trick, unfortunately.:cry:
Back