Recent content by LordWhiteley

  1. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    Yes weird that at the same time the plastic anchor holding the return spring broke off? Still it's all working perfectly now :) Just having fun & games trying to add Hive to my Home Assistant:(
  2. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    Ok a sucessfull update !! I swapped the 3-way valve for another one and the Central Heating now works perfectly :)) So many, many thanks to all those that helped my sort this out !! On examination of the removed 3-way valve, I noticed a rattling sound from something clearly loose inside and on...
  3. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    I can only explain this by saying the the Hive contacts are really bad at gripping the wires, no matter how tightly you screw them up. A couple were loose but I think they are definitely anchored in now.
  4. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    So I guess the next step is to fit another motorised head unit (I do have a spare) ?
  5. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    Yes the old wall thermostat is removed and is shorted out at the terminal block. Before I did this, I had set the old thermostat to maximum. Disconnect inv and shorting out at the terminal block made no difference to the operation of the CH.
  6. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    Sorry for my ignorance, do you mean the short at the end of the room thermostat wires?
  7. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    So do I :) I will double check the 3-way valve voltages and add to the table :)
  8. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    Here are the measurements of on Terminal 1 (Wire removed) :-
  9. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    I could try that next. So remove the wire from Terminal 1 and then measure the voltage on the Hive terminal?
  10. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    OK I did two things today. (1) I swapped over the LP241 but it still did the same thing ie CH On - only when HW on at the same time. (2) The second thing I did was measure the AC voltages on the terminal block at the back of the HIVE unit while connected :-
  11. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    Yes I missed that point . I'll try an measure the HW off, HW on & CH on the terminals on the back of the Hive control unit. If they match those measured on the 3-valve, in particular grey HW off - then the Hive unit is suspect - I also verify this by refitting the LP241 and seeing if CH on works...
  12. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    Well luckily I do have a spare Drayton MA1 3 position valve I can swap over...
  13. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    It would be real coincidence if the tank thermostat was faulty at the same time as swapping the hive unit. So I wonder if the hive unit is actually providing the HW off mains supply? I could try and measure this at the control box?? A faultly Hive unit would make the most sense?
  14. LordWhiteley

    Lifestyle LP241 replaced with Hive CH issue

    Interesting !!! so there is definitely a HW off connection on the controller terminal block. I wonder if there is a problem with the Hive unit? I will temporarily re-fit the LP241 controller and see what that does (CH should be on continuously as I shorted out the thermostat in the wiring box)