    Danfoss Motorised Valve

    when I press button on relay module ( receiver for room stat ) ( HC60NG ) when CH is being demanded from CH programmer the actuator clicks - but nothing else does this indicate faulty actuator / microswitch - I have dismantled and all looks good - motor moves smoothly - all connections...
  2. M

    Danfoss Motorised Valve

    yes, thanks for that. Easier said than done when you have 4 interacting components - two wireless in 3 different rooms - and when you don't know what you are doing - which is why I am here!!!
  3. M

    Danfoss Motorised Valve

    it's cold here!! Summary: Boiler seems ok - supplies hot water for HW storage cylinder. No response ( from boiler ) to demands for CH 3 way Valve seemed to be sticking so replaced - when I removed old valve it was very stiff - could not move ( with just fingers ) to or beyond...
  4. M

    Danfoss Motorised Valve

    it has a button when pressed it demands CH from system However - the system only "fires" for a few seconds ( pump/ actuator) then shuts down...
  5. M

    Danfoss Motorised Valve

    so - only having power to grey if CH & HW off is ok As I discovered - white ( B&W) powers on when stat demands ?
  6. M

    Danfoss Motorised Valve

    it's a wireless stat "Honeywell Wireless Room Thermostat Y6630D Stat"
  7. M

    Danfoss Motorised Valve

    as stated before - white ( actually from my actuator it is a black and white wire ) is NOT powered until room stat works..
  8. M

    Danfoss Motorised Valve

    FOrgive my ignorance - not sure what you mean here. Do you mean in the junction terminal box link orange to grey? grey to neutral? I'm guessing!!
  9. M

    Danfoss Motorised Valve

    ** yes - as long as room stat is activated ( red light on) the valve and pump turn on
  10. M

    Danfoss Motorised Valve

    sigh system seems to tire of my meddling and shut itself off after too many button presses!! for a while I had voltage at both grey and orange wires state 1: grey 240, white ( B&W ) 0, orange 0 state 2; grey 170, white 0, orange 240 state 3; short bursts of 240 on white when room...
  11. M

    Danfoss Motorised Valve

    SO - summary!? Programmer is live, sending HW and CH demans o tank and or room thermostat. room thermostat is sending signal to boiler, valve and motor ( or however the chain of command is ) - thunderbirds are go..... then not! If we assume ( for now ) that actuator, valve and pump are...
  12. M

    Danfoss Motorised Valve

    ""when CH demanded first valve has to move to CH ( and or HW + CH ) position, and this then mechanically triggers a micro switch to tell boiler to refer to room stat and decide to turn on boiler!! ? Read more: //www.diynot.com/forums/viewtopic.php?p=2905485#2905485#ixzz2hX4xefGr""...
  13. M

    Danfoss Motorised Valve

    ok - Not tested yet - still working through the logic. Neither the valve nor the boiler respond to CH demand I can force system to give me CH ( rads warm until HW storage stat turns off boiler. ) if I move valve lever manually to HW+CH ok - thinking on " out loud! " when CH...
  14. M

    Danfoss Motorised Valve

    ** Old valve was very stiff - could only just move it with pliers - New valve fitted move easily with just fingers ** thanks for detailed reply / trouble shooting guide!