Recent content by penguinventures

  1. P

    Aga Range - Gas Aga Flue

    On a recent change of Gas Engineer my Aga was condemned as there seems to be a plate missing from the outside balanced flue. The engineer is not experienced with Agas and cannot go further with any advice or supply of parts. Can anyone recommend a Gas Aga engineer in the Huntingdon Cambs area...
  2. P

    Boiler Overheat

    Thanks again for the support. If an auto bypass replaces the current gate vale there would be a bypass loop of over 12 metres. Hopefully this would be enough? I'm waiting now for a heating engineer to meet me at the property then it'll be clearer what is and what can be configured. Cheers
  3. P

    Boiler Overheat

    Cheers for the advice. I'll have a look for the terminal on the stat. Maybe its even wired in and become disconnected in the airing cupboard? If not hopefully there's already a spare core in the cable running from the boiler to the airing cupboard? From what I've seen of the Heat Exchanger...
  4. P

    Boiler Overheat

    I have a Myson Economist 60/80 S Plan system which has started to occasionally overheat shutting off the pilot light. Seems to occur only when pump stops when boiler is flaming at max output. Boiling/rumbling can be heard in the heat exchanger as there’s no pump-overrun and the overheat sensor...
  5. P

    Hoover Washing Machine HNL-7146 3 Flash Fault Code

    The machine does not fill with water when a wash is selected. It runs the pump to empty water and just cycles the drum back and forth. In diagnostic mode it shows error code 3 meaning:- Not drained in time allowed - washing machine fails to drain water Check that filter...
  6. P

    Gas boiler overheats on valve closure - vented system

    The automatic bypass valve was completely blocked with iron oxide. A different valve has been fitted which has a bigger bore. All is fine now.
  7. P

    Gas boiler overheats on valve closure - vented system

    I thought about the hasty response after I wrote the reply and thought it was an unfair reply - sorry. At the weekend, if I can close the isolator valves, I'll remove the motor and have a look. I've just watched the auto-bypass not flow. The rad valve closed. Temp above the bypass went to...
  8. P

    Gas boiler overheats on valve closure - vented system

    I think think the pump is ok. It sounds alright? It's less than 5 months old fitted straight after the powerflush. It's already on setting 3 which is what the plumber told me to leave it on. Currently the measurements either side of the auto-bypass are equal so there's currently a flow...
  9. P

    Gas boiler overheats on valve closure - vented system

    If there is anyone still following this continuing saga who's not lost the will to live... With the manual bypass valve fully open and the auto-bypass control fully wound out. I monitored the temperature either side of the auto bypass valve seeing a 10 degree drop. As the rad electric valve...
  10. P

    Gas boiler overheats on valve closure - vented system

    Currently the auto bypass is wound fully out and the old bypass is open too. Flow arrow is correct.
  11. P

    Gas boiler overheats on valve closure - vented system

    Yesterday I opened the old bypass close to fully open. Boiler has overheated twice. Any ideas what I do now? I have two thermocouple meters so can monitor other points in system.
  12. P

    Gas boiler overheats on valve closure - vented system

    Tony I confim; The motor valves close & the boiler stops firing. The pump continues to over run as its controlled by the boiler. Once the valves close that heat in the boiler is not always dissipated by the pipework and the overheat trips. I've setup two meters monitoring the boiler's...
  13. P

    Gas boiler overheats on valve closure - vented system

    I'll have to listen out for rumbles as you suggest. Not sure I've heard that. As you'll see from the photo posted the old gate valve is still there and can be partially opened. I'll open it partially this weekend see what happens. I'll also measure temperature differential across the boiler...
  14. P

    Gas boiler overheats on valve closure - vented system

    The auto bypass is adjacent to the pump in the airing cupboard which is 5 metres pipe length away. The boiler connections are 22mm - pipe changes to 28mm for the 5 metre run to the airing cupboard. Half of the run is exposed pipe high on the wall, other half is reasonably insulated (with a...
  15. Airing cupboard

    Airing cupboard

    Sorry you have to tilt your head!