Recent content by Red One

  1. R

    RCD tripping with EV charger..Question.

    good call, never thought of that, I will check it. Its easy to test by removing the pug and its cable from the charger and seeing if the charger then trips the RCD.
  2. R

    RCD tripping with EV charger..Question.

    Excellent. thats a straightforward and clear response, thank you. I know its not a faulty RCD in the CU as I bought a new one and replaced it with the same result. That was the first thing I checked. I will now check the supply cable from the garage CU with the EV charger disconnected and...
  3. R

    RCD tripping with EV charger..Question.

    Stop being a smartarse. I am full aware of what the RCD is doing and why. My query is how it seems to function normally with this earth leakage when the RCD is bypassed. Should there not be some other manifestation of a fault? I didnt suffer shock when testing it or doing a test charge on the...
  4. R

    RCD tripping with EV charger..Question.

    yes, I disconnected all wiring, including all the live wires from the MCBs, and all the neutral and earth wires from the bus bars. I then tested the EV supply cable in compete isolation from all other circuits on the CU. With the EV cable out of the equation, all the garage MCBs via the RCD...
  5. R

    RCD tripping with EV charger..Question.

    You need to read it again, I stated on the description. "I then went to the garage, as I suspected the issue might be in the CU thats installed there. The garage CU is covered by the RCD in the house, so only has a mains isolator at the garage CU". Again, this is how it always has been from the...
  6. R

    RCD tripping with EV charger..Question.

    Im not sure an electrician is left having to do so much and to be honest, if he couldn't get to the fault reasonably quickly, given that its clearly either the EV charger, or the cable from the charger to the garage CU thats at fault, Im not sure I would want to pay him to work on the issue in...
  7. R

    RCD tripping with EV charger..Question.

    Thankyou. I dont think the cable between the garage CU and the charger has developed a fault. Ive inspected the terminals and they are fine, and there are no kinks, rubs or breaks in the outer sheath. It hasnt been moved at all either in the 3 years to cause any sort of breakage. The armoured...
  8. R

    RCD tripping with EV charger..Question.

    Thanks. You are so helpful.
  9. R

    RCD tripping with EV charger..Question.

    All there is to see is a mains isolator, and 5 MCBs, 2 for lights, 2 for sockets and one for the EV charger. This is fed by an underground armoured cable from the house CU via an RCD switch. As I said, there have been no issues or even trips over the last 3 years and the EV has always charged...
  10. R

    RCD tripping with EV charger..Question.

    Thanks for that. But why would it have worked flawlessly for the last 3 years under the current configuration and not now?
  11. R

    RCD tripping with EV charger..Question.

    I have 2 CUs in my house, box one covering lights/ cooker/ machine etc. The other box 2 is for sockets, garage and a few other things. several days ago, the RCD for box 2 tripped. After spending quite a time checking all the cabling in the box I tried to isolate which MCB the issue might be...
  12. R

    Hot water from Tundish after multiple checks.

    Yes, I'm sure the EV is fine. It holds a charge ok and is only a few years old. I measured the pressure on the Ev bladder with 3 gauges. A new one I bought a few days back, 1 I already had, and the gauge on the tyre inflator I have for my compressor which is a heavy duty forecourt job. All...
  13. R

    Hot water from Tundish after multiple checks.

    The lower PRV was fitted years ago by a plumber who I had called in because our water pressure was causing a lot of noise when running taps etc throughout the house. When he came, he said our pressure was too high and fitted that lower PRV. I did not know the system as I would now to debate if...
  14. R

    Hot water from Tundish after multiple checks.

    John. I have attached the schematic from the Santon cylinder installation manual. It shows the balance cold water connection tee to come after the combo valve and PRV and before the EV tee. I have also attached a photo of the actual set up reflection those instructions with the balanced out...
  15. R

    Hot water from Tundish after multiple checks.

    Sorry John, you have lost me a bit there. The balanced cold is indeed teed off downstream of the combo valve and pressure release valve. Would this not be correct as effectively the cold supply to the shower and the hot supply are both pressurised to the same pressure as the cylinder? Are you...