Recent content by steve190

  1. S

    domestic ringmains

    Must be you :shock: Jobby - also known as a number 2 :lol:
  2. S

    Extending ring mains, cable sizes,voltage drops etc

    Just to start the ball rolling, as I'm sure the more learned will explain in greater detail. With a ring the load share between both halves of the ring. A 32a ring is can supply up to 100 sq m of floor space (OSG pg 151 (brown edition)). This is for a domestic location and takes into account...
  3. S

    Cooker circuit with junction box

    So long as the Jb is accessible, if required, for an inspectio & test and is rated to carry the current then no reason not to use one.
  4. S

    SET OF HALOGEN LIGHTS

    Are they rated for the bathroom?
  5. S

    cost of getting a CONSUMER UNIT put in

    towman. Will the suppliers fuse support the increased load?
  6. S

    ring main cable near heating pipe

    Re route the cables under the pipes
  7. S

    40 amp to 13 amp

    What rating is the shower? What size is the cable supplying the shower?
  8. S

    kitchen wiring

    I'd assumed that already from your earlier posting. Just so you understand. I misread 6.6Kw and typed 3.3Kw but I had already worked out that 6600/230 is 28.69565217 amps, so I rounded it up.
  9. S

    wire up shower to consumer unit

    Yes. Have you considered the need for suplementary bonding. Is it fitted? If so is it correct and what else do you need to do.
  10. S

    cooker control unit

    Is there a reason you're asking this again? What happens if the answer you get in this thread is different from the answer in the other? Which are you going to believe? And having fitted this cooker circuit are you going to test it?
  11. S

    kitchen wiring

    Whatever that means. At least the current is correct :oops:
  12. S

    Help identifying MCB (*Pics Added*)

    Sounds like a BS3871 MCB, the M6 indicating that it rated to 6000A short circuit current (this is not the overload current). These have been superceeded by the BS60898 (Type B, C & D). Without knowing its rating and the size/length of cable you are using/ plan to use for your shower and the...
  13. S

    kitchen wiring

    How long is the 10mm cable and how is it run? Under floorboards, through insulation? Before being able to say what a cable can carry we need to know its installation details. So the new hob is 3.3Kw (29Amps) and you want to use a 13Amp fused switch, how long do you think the 13amp fuse will...
  14. S

    spur query

    So from this I take it that it is impossible to plug two 13 amp plugs into a twin socket. And if each 13 amp plug had a 3 Kw radiant heater on the end it still only comes to 13 amps :?: Triple sockets are always fused? MK are but I don't believe to 2 to 3 gang conversion is.
  15. S

    spur query

    HOWEVER OSG states that an unfused spare may supply one single or one twin or one multiple socket outlet. So a triple takes us up to 39 Amps again. :roll: