Good spot on the pipe temp measurement. When I put the thermocouples in the boiler on the return next to the sensor they are low by ~5 degC. Going to have to first measure the return in the boiler manually to make sure it's the thermocouples that are wrong and then redo the calibration as some...
I removed the ABV and blanked off the pipework
That little grey line at 10 is d.15 Output of PWM pump in %. It's not totally reliably captured and it only has three values that I can see 0%, 45% and 100%. I think the pump only has two speeds so this would make sense and I'm still yet to test...
Well I didn't expect that.
Removed the external ABV and the effect this morning was that the boiler flow / return delta went from 8/9 degC to 10/11 degC but the return away from the boiler delta to the boiler return went from 13/14 degC to 6/7 degC
My assumption is that the external ABV was...
This may show the difference better. 1 cycling still has demand so boiler flow and return track down towards pipe return temp. Third cycle where the demand is removed and zone valve closes the boiler flow and return reduce slowly as the water is recycled through just the bypass
I think your seeing a data capture timing issue in the bottom one as the capture of flow and return were at different times. I've sorted the issue out in the top one so there should be only a couple of seconds between the measurements.
The lines at the bottom of the chart give radiator, UFH and...
You house probably uses a similar amount of energy to mine (10 rads + 2 rooms with UFH) and much of what you said is where I was trying to go. Unfortunately my boiler as an older model and can only modulate down to 12kW which is above the usage of the house most of the time.
Once I fix the...
Tried setting d.1 pump anti cycle to 10mins (from 5) and d.2 burner anti cycle to 60mins (11.5mins for 65 flow target) from 20mins
It looks like it is cycling over 12 mins period and pump running for 9/10 mins after burner switching off so only 3 min burn at a time
This is slightly better than...
The ABV is one of these Honeywell DU145 ABV
The test was with just the radiator demand on with probably most of the TRVs open. The ABV says it is set to 6 bar but the top comes off of it so I've tightened it until I can feel it click which I assume is now at 6 bar
Well wasn't expecting that. Looks like the external bypass is letting the flow through.
The temperature just after the bypass is near enough the same as the boiler reported return temperature and not the same as the return temperature from before the bypass about 50cm away from it
I wonder if...
Not sure if this will help but we have an similar unvented HW cylinder but we have put an additional old school insulation jacket over it as well as the foam that is on the HW cylinder.
At the bottom of the cylinder it looks like it looses 5 degC in 3.75 hrs
That matches the document I have that came with the boiler. I'll try the things suggested to see if it makes it any better.
I'm also thinking that a weather compensation controller is a waste of money as when it changes the flow set point the boiler wont be able to modulate below 12kW and will...
Setting d.19 = 1 should mean that everything is on low speed but I'm not sure if there is any way to check pump speed?
I have a slight worry about the external ABV and was going to remove it to make sure it wasn't the cause as the pipe the other side of it is hot but that could just be...