  1. Y

    Danfoss cylinder thermostat problem

    I installed a new programmer last week and everything has been working as it should ever since. So the problem was a faulty switch within the programmer. Thanks to all who contributed to this thread.
  2. Y

    Danfoss cylinder thermostat problem

    To recap, When my programmer is switched off at both the heating and hot water buttons the boiler will fire up on its own. The only way I can turn the boiler off is to turn the cylinder thermostat down to near zero. What I have determined from this thread is that the dhw switch within the...
  3. Y

    Danfoss cylinder thermostat problem

    EFL yes it did go off again. AlanE Boiler wiring diagram attached. I don't think the boiler has a switched live. Do you agree?
  4. Boiler wiring diagram

    Boiler wiring diagram

  5. Y

    Danfoss cylinder thermostat problem

    When I got the dead readings at 8 and 14 the cylinder thermostat was turned down to zero. I just turned the thermostat up until I heard an audible click in the thermostat. Checked 8 and 14 again. Both were live. (and the boiler fired up)
  6. Y

    Danfoss cylinder thermostat problem

    Thanks you for all your help. I shall organise a new programmer and post back when i have fitted it :D
  7. Y

    Danfoss cylinder thermostat problem

    I stuck the screwdriver in as requested. 8 dead, 14 dead, 15 live. I removed the programmer from the back plate and 10 and 15 are now both dead. (I did remember to turn the power back on at the spur after removing the programmer from the face plate) Faulty programmer looks more certain...
  8. programmer back plate

    programmer back plate

  9. Y

    Danfoss cylinder thermostat problem

    OK. I stuck a mains tester screwdriver in terminal 10 with the programmer switched off and the atc cylinder stat at zero. I am getting power. So I switched wires 4 and 8 on the junction box and physically switched heads on the motorised valves to check if the hot water valve was sticking...
  10. Y

    Danfoss cylinder thermostat problem

    Thanks for that EFL. Yes I have used the earth wire for room stat to terminal 2.
  11. Y

    Danfoss cylinder thermostat problem

    Is this OK?
  12. junction box

    junction box

  13. Y

    Danfoss cylinder thermostat problem

    Don't know why the photos didn't display in the comment box, but if you click on my user name they are in the album "danfoss".
  14. Y

    Danfoss cylinder thermostat problem

    RF,here are photos of the junction box, thermostat and programmer wired connections. Andy, atc wire terminal 2(nc) goes to junction box terminal 14 which has a permanent link to terminal 8. The brown wire from the dhw motorised valve goes to 8 on the jb, so these two are connected. atc...
  15. programmer

    programmer