Hi, got a baxi 105e combi boiler and the pressure gauge reads 2bar.

The problem no hot water or heating.

The fan on the flue turns very slightly when boiler turned on then stops, it turns freely by hand.

Any idea of the reason for the fan not running ie fan motor gone or the power to the fan at fault ?

Thanks all.
 
Sponsored Links
is pump running , is pin coming out of TOP of divertor and activating the microswitch, are you getting 240v at fan terminals.
 
Check power to fan when a demand called for. You should get 240vac.

If its constant 240 to fan but its not runnin motor is guffed, if voltage drops away then either the board is failing or the pressure switch is dropping out.
 
Sponsored Links
Hi all thanks for your feedback re-confirming the symptoms.

No Heating or Hot Water.
Water pressure ok.
Flue fan not running.
No power at the fan.

Will post again very soon with the remedy.

Good luck all.
 
Thanks a lot will post if the p-switch is stuck and confirm your remedy asap.
 