check valves in heating system?

Joined
15 Apr 2008
Messages
109
Reaction score
3
Location
Derbyshire
Country
United Kingdom
I have installed a four zone system, but I have made what appears to be a school boy error. Basincally, I have three CH zones, upstairs, downstairs and conservatory, and a DHW zone, all connecting back to a common return. However, when the downstairs CH is selected, the upstairs rads slowly come on as well. I seems that at one of the upstairs radiators, the returning downstairs CH passes through the upstairs radioator via the return, thereby pressusing the supply side of the upstairs rads! Should I have fitted check valves on every radiator (or at sensible places on the return system) to prevent this? Can I get a combined non-return/lockshield for each radiator? Any ideas appreciated!
 
Sponsored Links
Cant see anything wrong with the pipework. Zone valves on each supply leg, but common return. The only way to stop this would have been to have had seperate returns all the way back to the boiler - neither practical nor economic, surely?
 
Sponsored Links
Logic would suggest that if the pipework was 100% correct, the system would function 100% correct. I have never seen a system that was piped up correctly where there was a need for check valves. Maybe Bahco is right.
 