I have a 10mm T&E cable on a solid brick wall under a steel channel running from the ceiling to half way down the wall and then exiting through the brick wall to a 32A 7.4kw car charger that may run for several hours at a time. It's on a 40A MCB.
I'm looking to install wood fibre internal wall insulation on this solid brick wall and the insulation will likely be about 75mm thick, certainly less than 100mm.
If the cable was left in place and the insulation placed over the top of it presumably the cable would be derated but what derating reference method should be used to work out by how much it is derated?
If needed the cable could be moved away from the brick to in front of the insulation and just behind the plasterboard in which case I think would be method 102 would apply?
Alternatively as it's sandwiched between brick and insulation do they class the brick as insulation in which case method 103 would apply.
Any thoughts?
I'm looking to install wood fibre internal wall insulation on this solid brick wall and the insulation will likely be about 75mm thick, certainly less than 100mm.
If the cable was left in place and the insulation placed over the top of it presumably the cable would be derated but what derating reference method should be used to work out by how much it is derated?
If needed the cable could be moved away from the brick to in front of the insulation and just behind the plasterboard in which case I think would be method 102 would apply?
Alternatively as it's sandwiched between brick and insulation do they class the brick as insulation in which case method 103 would apply.
Any thoughts?