I currently have to install 2 heaters. One heater outside an enclosure which is self heat regulated and one inside the enclosure which will be controlled by a thermostat.

The external heater has a running current of 1A.

The internal heater has a running current of 0.5A, but has a switch on current of 6A for about 1sec. As this will be happening fairly often because of the stat controlling it, I need to spec the MCB accordingly.

Can anyone tell me what size I should use and what type 'B', C or D type MCB?
 
Sponsored Links
Sponsored Links
I would use a 10A type B for that.

You might get away with a 6A type C or D which might withstand the surge you mentioned but it's not worth the mither.
 