I have a problem with the water pressure, it keeps rising to 3 bar over the course of 4-5 days,the filling loop is a worcester bosch part and is closed with the key removed,the system was flushed when fitted so should be clear of crud,the whole installation is just over a year,any ideas please. :rolleyes:
 
Sponsored Links
The water pressure in the heating - is it related to the heating being on? I guess in this weather you have not used the CH?

Therefore the rise in water pressure is most likely a cross contamination leak in the boiler..... which should be under warranty if it was fitted professionally.
 
thanks for that i'll look into warranty,if not any idea what part may require cleaning if i have to find a approved plummer,it takes around two days to reach 3 bar heating on or off
 
Does the pressure rise when system is hot or cold. if when hot then expansion vessel fault. if when cold filling loop leaking by
 