need for shower cross bonding

Joined
1 Apr 2008
Messages
1,185
Reaction score
202
Location
Devon
Country
United Kingdom
hello all

thanks in advance for your responses

When putting in a 10.8 kw electric shower

with plastic pipes running under (tanked) floor and behind tiled walls.

should the cross bonding in the room be connected to the earth terminal on the shower?

If not, or instead, should it be connected to the shower earth lead at the shower isolation switch (just outside the room)


cheers

Stephen
 
Sponsored Links
It needs to connect to the shower circuit earth. If it's easier to do it at the switch, then do it there.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top