Never rely on low-voltage meters for IR values.
Indeed - that's what most of this discussion (and the included illustrations) has been emphasising. The voltage used for testing is only really an issue if one is measuring something which is not a 'simple/straightforward resistance' - but the sort of causes of measurable IR in electrical installations are often not 'simple/straightforward resistance' - so you comment is clearly true in terms of that sort of measurement
When testing IR you are measuring leakage currentThink of it like this: ... You have a bicycle tube that you need to test for leakage. The normal pressure is 30psi. You immerse the tube in water and pump it to 1psi. You dont see any bubbles so there are no leaks right??? WRONG. You then pump it up to 30psi and see a few small bubbles. Then you give it 60 psi and see air p******g out.
You make it sound as if 'the problem' arises because what one actually measures is leak leakage current, which obviously varies with testing voltage, but that is not really a problem. With your analogy, if it were a rigid container with a small hole in it, then (ignoring some minor 'clever complications'), then the rate of flow through the hole would be directly proportional to the pressure within the container - so, provided only that one has a sufficiently accurate means of measuring flow (aka current) one will get exactly the same answer (for 'resistance of the hole') whether one uses 1psi, 30psi or 60psi.
Returning to electricity, if one has a 'simple straightforward resistance' (e.g. a carbon resistor), which is analogous to the 'rigid container with a hole', then (again, provided only that you can accurately measure the current) you will get exactly the same answer for the resistance whether you measure with 1000V, 100V, or 1V. ... anyone can confirm that for themselves - measure a 1MΩ resistor and they should get the same 1MΩ answer with their 1000V IR meter/MFT, a 9V (or 3V or 1.5V!) multimeter, or any testing voltage in between.
What your analogy helps to illustrate is that resistances may not be 'simple and straightforward'. So long as the pressure in it is high enough to more-or-less maintain it's normal inflated shape/size, then, as above, you should get exactly the same answer for 'resistance of the hole' more-or-less regardless of what pressure you use. However, at very low pressures, the tube will start to collapse, ultimately to the extent that flow of air out of the hole will (for a given pressure) be reduced, possibly even to zero - so the measurement of 'resistance of the hole' (by dividing pressure by flow through the hole) will no longer be a correct reflection of what the resistance would be at higher pressures. The measured resistance is
not 'incorrect - it's correct for the pressure at which it was measured (since the resistance has actually been increased by the partial occlusion of the hole at low pressure), but not the same as it would be if measured at higher pressures.
This is analogous to the deviation from a linear voltage/current relationship (i.e. deviation from Ohm's Law) which can occur when one is talking about something more complicated that a 'simple resistance' - e.g. when electro-chemical processes are at work due to fluids, electrolytes or corrosion, or when materials (e.g. insulation) undergo voltage-related changes, such as (temporary or permanent) dielectric breakdown. However, again, the 'high' result one might get by measuring with a low test voltage is not 'incorrect' - it is merely lower than it would be in the face of higher voltages (which is what one usually wants to know about!).
The reason for testing at higher voltages (ie500V) is that some leaks only appear at higher pressures. Think of a tap that was fine until the supply pressure was increased and then a small dripleak was spotted. Reduce the pressure again and the leak disappears. It does not mean that it is fixed.
Indeed - that's another example of a 'non-simple' resistance - the washer may 'stick' to it's seating until a certain pressure is present, thereby again creating a non-linear pressure/flow relationship. However, if the leak/drip were through a pinhole in the pipe, we would be back to a more-or-less linear situation, such that the rate of flow would be more-or-less directly proportional to pressure - so that, again, 'resistance of the pinhole' calculated by dividing pressure by flow ought to be much the same for any pressure (within reason!).
However, all that aside, I think we are all agreed that one cannot trust 'IR' measurements of electrical circuits or components that are undertaken using test voltages below their normal (peak) operating voltages - hence, even 250V DC is not really high enough for circuits/components designed to work at 230V (RMS) AC ... hence most routine IR tests on 230V circuits/components being undertaken at 500V.