I can only refer you to 412.2.3.2.
Interesting. I didn't realise it was 'duplicated', and wonder why they bothered about that one, which relates only to circuits supplying Class II equipment. The one I'm familiar with is (the last paragraph of) 411.3.1.1, which says exactly the same but for
any circuit (hence including those mentioned in 'your' one)!
It seems very simple to me. You are free to ignore it, should you wish.
You may regard it as simple, but it's what we've been discussing. You presumably disagree, but my inclination is to regard
all of the cabling of a circuit from the CU/DB up to where it enters an item of "fixed equipment' as being 'fixed wiring' - which (in view of the Part II definition of a 'point') would lead me to a different conclusion from yours.
If, for some reason, the (3-core) supply cable from the switched lighting circuit was, say, 30 cm too short to reach into a Class II item and I therefore extended it with a JB and short length of cable, I presume you would agree that that extra bit of cable was still part of the 'fixed wiring', and therefore that it had to include a CPC. It just seems a little odd to me that if that 'short extra bit of cable' was installed in the factory, it ceases to be 'fixed wiring' and therefore arguably does not need to have a CPC.
I have no desire to ignore either those regs and, indeed, there are very few situations in which one has any realistic opportunity to ignore them. I merely asked whether it was strictly compliant to have a situation in which the cable entering a Class II item had no CPC. As I keep saying, I'm trying to learn, not argue.