30amp to 45amp

The idea being that a board with a sub-100A main switch is not designed to carry loads above 30/32A.
 
Sponsored Links
And a board with a 100A main switch can only carry one fuse greater than 30A/32A
 
Well, certainly the older Standard Wylex range.

That is my rule of thumb, not to put more than one >32A circuit on any one 1P board, but having spoken to manufacturers of modern din-rail-based units, they don't seem to object to more than one large circuit on one board.

Even Hager, whose split-load RCD's are still rated at 63A, didn't bat an eyelid when I asked whether two 40A circuits could be connected through the same RCD.

Imagine 2 x 9+kW showers on one RCD and whatever else was on at the time....

Personally, I think split boards should have an RCD rated the same as the main switch.
 
Sponsored Links
you will need to seek the services of a professional because the likely work is illegal as a DIY
This is untrue - no DIY domestic electrical work is illegal; it's the failure to notify that's against the law.
 
jazzy1963 said:
the cable is approx 14mm wide...
As this cable sounds like it is actually 6mm then your 30A fuse blowing is doing exactly as it is supposed to - protecting the supply cable to the shower.
 