That is my rule of thumb, not to put more than one >32A circuit on any one 1P board, but having spoken to manufacturers of modern din-rail-based units, they don't seem to object to more than one large circuit on one board.
Even Hager, whose split-load RCD's are still rated at 63A, didn't bat an eyelid when I asked whether two 40A circuits could be connected through the same RCD.
Imagine 2 x 9+kW showers on one RCD and whatever else was on at the time....
Personally, I think split boards should have an RCD rated the same as the main switch.
As this cable sounds like it is actually 6mm then your 30A fuse blowing is doing exactly as it is supposed to - protecting the supply cable to the shower.