I have a basic LCD panel - 3 active zones. I nolonger need zone1 as this was on a door that has been replaced. So i need zone 2 to be the timed entry PIR. I know the engineers code. But cant figure out the logic to reprogram, when I look at the manual. thank you
Yes they will be numbered on the pcb. Fit wire link across zone 2, and dont forget to disconnect the door contact from the global tamper (if it is wired in)