Apollo 30/50 boiler

Joined
13 Mar 2006
Messages
1
Reaction score
0
Location
West Midlands
Country
United Kingdom
My Apollo boiler pilot light will not stay lit permanently. I have changed the thermo couple and the overheat stat but still no joy. I can light it and the boiler functions normally but two mornings out of three the pilot light is out so no heating. Tried to light it today and whilst it will light when I let go of the gas valve out goes the pilot light. Any ideas?
 
Sponsored Links
Faulty Gas Valve

Blocked Pilot

Poorly positioned t/lead

Possible circulation problem and o/heat stat is functioning to prevent the boiler boiling up. (Does seem unlikely as pilot will not stay lit now)

When was the appliance last serviced?

David
 
If not serviced properly, another thing Apollos do is 'blow themselves out'. IOW, when the burner attempts to light up, the flame fails to propagate across the burner, the thing fills up with gas, there's a loud bang from 'delayed ignition and the pilot light gets blown out.
Get it serviced!
 