I was going to post this in the RGI forum but i'm interested in the views from the BG lads.
Got a call earlier from the in-laws saying the boiler smells funny so i said i'll be there. The boiler was a BG install and 5 star covered untill just before christmas.
Quick look at boiler and soot is visable on the bottom of the burmer tray so to cut along story short after stripping down to the heat ex i'm by a large block of soot.2 hours later and 5Kg of soot the heat ex is clean.
Burners is stripped and found clean as a whistle,injector checked but clean. Gas valve in good working order and regulator functioning and mid range and gas rate matches data plate. FGA is 0.0002. Flue and vents all good, so basicalyy nothing to sugest why we have a large sooty HX.
Mother in law is a nice but untrusting kind of person(watches everyone doing anything in their house) and commented that no BG engineer has ever removed burner case and cleaned/inspected the heat ex. the last 3 BG services only took 15mins(For an openflue )
the checklist states all radiators warm ok, no leaks but the enginner recommends a powerflush(no problems reported and no samples taken),so not only can he not service an appliance he likes to rip you off by recommending things that as far as he is aware aren't needed.
I'll be ringing the service manager tomorrow any other comments or suggestions.
Lee
Got a call earlier from the in-laws saying the boiler smells funny so i said i'll be there. The boiler was a BG install and 5 star covered untill just before christmas.
Quick look at boiler and soot is visable on the bottom of the burmer tray so to cut along story short after stripping down to the heat ex i'm by a large block of soot.2 hours later and 5Kg of soot the heat ex is clean.
Burners is stripped and found clean as a whistle,injector checked but clean. Gas valve in good working order and regulator functioning and mid range and gas rate matches data plate. FGA is 0.0002. Flue and vents all good, so basicalyy nothing to sugest why we have a large sooty HX.
Mother in law is a nice but untrusting kind of person(watches everyone doing anything in their house) and commented that no BG engineer has ever removed burner case and cleaned/inspected the heat ex. the last 3 BG services only took 15mins(For an openflue )
the checklist states all radiators warm ok, no leaks but the enginner recommends a powerflush(no problems reported and no samples taken),so not only can he not service an appliance he likes to rip you off by recommending things that as far as he is aware aren't needed.
I'll be ringing the service manager tomorrow any other comments or suggestions.
Lee