Biasi M90 32s fault

Joined
18 Apr 2011
Messages
39
Reaction score
0
Location
Lancashire
Country
United Kingdom
Hi could some advise the fault with my boiler.

It has started to make a buzz sound just as it should fire up but doesn't.

The electronic diagnostic lights show no errors.

Could the relays be not latching? Hence may point to the ignition board? (wanted to attach a video of the fault)

Any help on the matter is greatly appreciated.

Also noticed that the boiler has started to leak again at the gland nut six months after replacing switch, Gland nut, diaphragm. Do you suggest a new diverter valve kit or replacement diverter valve?

Thank you

Grover
 
Sponsored Links
Leaking gland nuts are caused by a dirty system. Or the pin was not cleaned when a new gland was fitted.

Is your boiler one with two PCBs?

Tony
 
Hi Tony I cleaned stem but it made not difference and yes it has two pcbs.

The system hasn't been cleaned so it could do with that.

Grover
 
You have to clean the pin WHEN the gland is renewed!

Where is the buzzing coming from?

Tony
 
Sponsored Links
Hi Tony

I cleaned it with some fine sand paper but it still failed.

The buzz sound is coming from the relays on the ignition board and upon feeling them it seems to be coming from the middle relay.(sorry for not explaining it right well)

I have a 3 second video clip of the fault but can't upload here because only accepts image.


Grover
 
In that case its most likely to be the ignition PCB.

I would have to charge £190 to replace the PCB and service the boiler!

Tony
 
Thank you Tony for help with the diagnosis and also the guide price for the repair.

Thank you

Grocer
 
Hi Tony

I have had the ignition board replaced and found that it fired up momentarily but doesn't.

Upon checking diagnostic everything seems ok. After checking voltages from the the regulation pcb it sends voltage to the ignition board for a split second fan is powered then the boiler doesn't lock. With diagnostic lights are as if boiler is operating normaly.

Visual inspection of the regulation board shows the relays not latching with a arc.

Any help is greatly appreciated

Grover
 
Can you post a photo showing the gas valve as viewed from the front of boiler?

Tony
 
Thanks for that photo.

I was wanting to see the three wires which come down from the combustion chamber in the centre.

But these three wires dont appear in your picture?

Who changed the PCB?

Tony
 
Hi Tony please find the image with the wires showing

Also noticed that when the pump connector is removed from the pump the boiler fires with no problems. This was only done for a split second to test the outcone only.


Grover
 
Boiler fires with out the pump runnung ?? well it should not fire at all !!
 