combi boiler problem

Joined
24 Jan 2004
Messages
4
Reaction score
0
Country
United Kingdom
I have a halstead quattro/wickes combi 2000,the hot water temp is low..with c/h off,h/w tap on..boiler will light and stay lit,but water is cold.With c/h on..h/w tap on water is hot for 10 seconds..then is warm(not hot enough for a bath)c/h works fine,water pressure is fine,boiler runs at 1 bar
 
Sponsored Links
Thanx for your reply,oilman.Do you mean the divertor valve?,I have checked that,the plunger moves up,and stays up when the h/w tap is on,then drops down when tap is off,any more suggestions,cheers
 
Still sounds like diverter valve. With everything cold (!) turn a hot tap on and grope the pipes under the boiler. One of the fat ones will be the flow pipe - written underneath usually. If the flo gets hot , it's the DV which isn't steering boiler water to heat the hot tap water. Can happen even if the shaft IS moving.
 
Sponsored Links
Does that valve feed water to the heat exchanger? I don't know anything about gas boilers, but I was thinking there might be a motorised valve Looks a bit like this
30424_l.jpg
 
ChrisR said:
Still sounds like diverter valve. With everything cold (!) turn a hot tap on and grope the pipes under the boiler. One of the fat ones will be the flow pipe - written underneath usually. If the flo gets hot , it's the DV which isn't steering boiler water to heat the hot tap water. Can happen even if the shaft IS moving.
Chris r,you are a star!,did exactley what you suggested,you were a 100% correct,fitted new d/v valve today...and enjoyed a lovely HOT! bath,thank you so very much.
 