    Hi;

    I have nearly completed my kitchen, the last two jobs are fitting a cooker hood for my 110 Range Cooker and Tiling.
    The Hood will be set up to extract cooking fumes through an outside wall.
    It is a Stoves:
    http://www.rangecookers.co.uk/stoves-1100trc-product,423.aspx

    The instructions for the hood (which are very sparse) says to drill a 130mm hole. The Extractor Adaptor which comes with the hood, on which I presume a hose is fitted, has a diameter of 116mm.

    The hole is being drilled through the wall on Tues and I need to work out exactly where the hole is to be drilled and have everything ready to fit the hood.

    What do you recommend using to direct fumes from the extractor adaptor through the hole. I have read that flexible hose should be used however a solid shaft should be installed in the wall.

    Any ideas what to get and where to get what I need, I have a Wickes, B&Q, Homebase, Focus, Travis Perkins and Jewsons.

    Ta
     
  2. hotrod

    Joined:
    26 Dec 2007
    Messages:
    1,162
    Thanks Received:
    110
    Country:
    United Kingdom
    Hi Skavenger, I used a Marley 125mm extraction kit which I got from B&Q to do mine. This would be fine for you too. But be warned, they don't carry the required "accessories" (for additional bends etc). You won't need to drill a hole either, as you can see from the link it's a brick sized vent, so a lump hammer and brick chisel and you're away.

    If you struggle to get a jubilee clip big enough for the flexi hose / spigot connection, just use duct tape - I had to, it's been fine. :cool:

    hth
     
  3. Skavenger

    Joined:
    4 Jan 2006
    Messages:
    127
    Thanks Received:
    3
    Location:
    Devon
    Country:
    United Kingdom
    OK I have trawled the various DIY outlets in my area and cannot seem to find exactly what I need.

    The Cooker Hood Extractor adaptor that is supplied with my hood is here:
    http://i38.tinypic.com/2meeu4l.jpg

    The dimensions seem to be non standard, well at least for all the various hood extractor bits that I can find anyway.
    The external dia is 118mm and the internal dia is 115mm.

    All the extractor supplies that I can find are based around 100 or 125mm.

    My extractor will be routed directly through an external brick cavity wall.
    Most Flexi hose is 100mm or 125mm.

    What I need to know is:

    1. Do I or do I not need to sleeve the hole in the cavity, if so what with.
    2. Most ducting seems to come in 100mm or 125mm sizes, my adaptor is neither, 125mm is slightly large for my extractor adaptor but will dropping to 100mm cause a problem?
    3. Wickes and B&Q supply an Easyfix wall duct which comes in 100mm and 150mm flavours here: http://www.wickes.co.uk/Easyfix-Wall-Duct/invt/199812 is this something I should use although it would seem that it is designed for an extractor to be bolted directly to it.
    4. Any idea how the above fixes to the wall it comes with 2 x screws on either end.
    5. Wickes also supply a 100mm x 320mm plastic sleeve that could be used to sleeve the hole. I had a play in the shop and it seems to fit nicely onto an outside wall vent, I could use it with some sort of a coupler at the other end to fit the flexi hose onto with a couple of jubillee clips.
    5. If I fit the sleeve above the 100mm flexi hose is to large to run through it?
    6. The only piece of kit that I could find that fits snug with my extractor adaptor is a reducer that is supplied with a DESIGN AIR kit supplied by B&Q but the reducer is for something else. It comes with an external vent, a 1.5m 125mm flexi hose, 2 x Jubilee clips and couple of adaptors.

    Am I making a simple job very difficult!!!
     
  4. ^woody^

    Joined:
    3 Sep 2006
    Messages:
    13,758
    Thanks Received:
    1,394
    Location:
    Birmingham
    Country:
    United Kingdom
    Use 110mm soil or underground pipe and fittings as appropriate
     
  5. Skavenger

    Joined:
    4 Jan 2006
    Messages:
    127
    Thanks Received:
    3
    Location:
    Devon
    Country:
    United Kingdom
    I have just re read the hood instructions and it specifies 125mm ducting!
     
  6. ^woody^

    Joined:
    3 Sep 2006
    Messages:
    13,758
    Thanks Received:
    1,394
    Location:
    Birmingham
    Country:
    United Kingdom
    It wont matter, its only a very short distance of duct
     