The point of all this is to take a step back and understand the basic principles of why bonding is required (whatever name you wish to put to it), it's not about blindly following a book but working out the implications of fitting it or not.
With PME, as I keep commenting, it is all about the Faraday Cage.
Understand how that works and you will "get it"
I really think that I do understand the principles, and that is, indeed, one of the things which causes me some problems.
As you've probably seen, I am far keener on bonding exposed metalwork together than many of the people here (who will often say that it's not necessary). However,as far as I am concerned, what interests me is my 'local Faraday Cage' which essentially relates to two or more pieces of metalwork close enough for me to touch two or more of them simultaneously. I create that local cage by bonding every bit of metalwork together. What I struggle to understand is why the creation of that cage is in any way helped or enhanced by not only bonding the metalwork together, but
also bonding it to the MET (i.e., with a TN supply, the DNO's provided 'earth').
I thought that, again with TN systems, the whole idea of BS7671-style 'main bonding' to incoming services was to ensure that the house could not simultaneously contain a true earth potential and the DNO's earth' (which, under certain fault conditions could be way above true earth). If no metal service pipes enter the building from outside, there does not seem to be such a risk to protect against.
Furthermore, as I frequently say, where I really do struggle is to understand why there is a requirement for 'main bonding' with a TT system (i.e. a piece of 10mm² G/Y joining together what are effectively two earth electrodes). The chances of a service pipe introducing a potential appreciably different from the potential of the earth electrode must be vanishingly small. Again, I would have thought that 'local Faraday Cages' were all one needs for personal safety.
Kind Regards, John.