17ed IEE Regs: Do you need two seperate 10mm2 cables or can you run one and cross bond
unbroken , Not even Crimped ,
unbroken , Not even Crimped ,
Got a reg number for that, LuckyP?
Yes, but NIC peeps not in charge.'twas what we were told to do by the NiC peeps, unbroken if covering both services and thus if either bond is disconnected the bond is retained for the other. If the 1st point was disconnected and was a separate cable on then no bonding to either service would exist.
part.Not even Crimped ,
me thinks you missed my point!! surely if water is 50" from electric meter and the gas is 25' away but in the same direction then the single cable can still serve bothBecause the bond should be made within 600mm of the service entering the building but after the stop tap/ gas meter. So ideally they need to be near each other.
In the case that the service are in the same directional route, it would be okay but if they are in different directions, you would use two, to save on material costs.