electric oven

Joined
21 Jul 2002
Messages
16
Reaction score
0
Country
United Kingdom
im fitting single oven power max usage 2.07kw fuse rating 13amp can it be connected using normal twin and earth cable and normal 3 pin plug ? does it have to be earthed sepratly
 
Sponsored Links
You can connect up to 3kw safely to a 13 amp 3 pin socket.

Ensure that you use a good quality plug, and that the socket is connected as part of a ring main, preferably.

For interest W=V*I, so I=W/V.

Therefore in this case I=2100/240=8.75Amps
 