Can any one advise me on how to test the APS on a Ferroli F30.
Reason... the boiler keeps dropping the burners out after running for 10-20 seconds but if you bypass the APS then ithe burners stay lit and boiler runs and appears to modulate just fine. The manual speaks of the air pressure differential (flue inlet to outlet) having to be greater then 180 pascals which I understand the reason for but how do I check this.
BTW Fan appears to be running OK and is clean, venturi clear as are the the air pressure tubes to the APS.
Reason... the boiler keeps dropping the burners out after running for 10-20 seconds but if you bypass the APS then ithe burners stay lit and boiler runs and appears to modulate just fine. The manual speaks of the air pressure differential (flue inlet to outlet) having to be greater then 180 pascals which I understand the reason for but how do I check this.