Fuse blown on Danesmoor 15/19 now no live feed to Water Pump

Joined
11 Dec 2012
Messages
3
Reaction score
0
Country
United Kingdom
Having replaced the fuse in the main switch on my oil fired central system the boiler works fine so we have hot water, however the water is not being pumped around the system.
 
Sponsored Links
Replace pump.

Check 240volts to pump. If pump has power but is not turning replace pump.

Sorted
 
Replace pump.

Check 240volts to pump. If pump has power but is not turning replace pump.

Sorted

I made the assumption it was the pump and replaced it however still no go, have today given old pump mains feed and it works fine. I have found there is no live feed to the pump ( terminal 4 on appliance terminal block )
 
Replace pump.

Check 240volts to pump. If pump has power but is not turning replace pump.

Sorted

I made the assumption it was the pump and replaced it however still no go, have today given old pump mains feed and it works fine. I have found there is no live feed to the pump ( terminal 4 on appliance terminal block )

You have a faulty 2 or 3 port valve in the system not sending live to the boiler.
 
Sponsored Links
Think I have sorted it , time clock fault , possibly caused by putting 13 amp fuse in before I realised it should be 3amp.
 