A 30A BS3036 fuse will take 60A for 100s and 50A for in excess of 10000s (2hrs 46mins) before rupturing.
Dont these things blow quite often with such a low current rating?
if you think about it.. the largest things in your house will bw the cooker and showere, both of which aren't likely to be on full load for any protracted period of time
2.5mm2 copper in free air can probably take as much as 200amps before it melts. Obviously when packaged as T/E it would melt it's pvc sheath before then, but the maximum current carrying figures you get in tables found in electrical regulations have quite a bit of headroom in them too.and if you can push 50A thru it for quite a while that could cause damage to the 30A feed wire (or for example the 2.5mm T&E in a domestic ring)?