Main equipotential bonding

Joined
22 Oct 2011
Messages
5
Reaction score
0
Location
Sheffield
Country
United Kingdom
I can't see any evidence of main equipotential bonding to the water and gas pipes entering my house.

I have checked the resistance between the main earth terminal and the pipes and the resistance is less than one ohm, but i'm a little alarmed that i can't see the connections.

Could the resistance measurements be this low if there was no equipotential bonding?
 
Sponsored Links
A low reading can be possible via the cpcs of appliances connected to water and gas (boiler being the prime example).
Although not set in stone there is a rule of thumb suggesting that 0.05 Ω is a low enough resistance between the MET and extraneous conductive parts.
A 10mm² connection is required to ensure proper bonding, especially if you have a PME supply.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top