hi helpers, ive just put some ceiling lights up without reading the instructions ! the lights keep tripping out when i read the instructions it read as follows " the torodial transformer used in this product may induce switch surges which can cause nuisance tripping of some circuit breakers if this happens seek advice from an electrican to change the C B on the household wiring to one suitable for inductive loads !
the MCB is 5 amp would upgrading it to 6 amp solve the problem ? easy to fit ? or shall i just return the lights to the shop !! as an adder ... im planing to put a immersion heater in . do i need a 20 amp MCB ? thanks