I have tested the fan wires(the two purple wires connected to fan) again with a multi meter.
If I disconnect wires from fan and connect to meter individualy ie +prong on fan wire and negative prong to earth I have 240volts on one wire and near zero on the other.
If I connect meter in situ with the wires connected to the fan and test each wire individualy to earth, then I have 240volts from each wire.
If I test in situ with the wires connected to the fan with one prong of meter on each wire, then it reads zero volts.
Does this sound right and which is the correct method to test these wires?
Any help greatly received.
Thanks in advance.
Dave