tabs said:
The burner pressure stays at 5 mbar for both DHW and CH.
The correct max pressure is 16.3mBar and minimum 1.5. Are you sure you are reading the guage correctly?
Since you are part way qualified it is your boiler and you have a u guage.
Are you puting u guage on correct part of gas valve, remember working pressure and standing pressure are taken from test point nearest incoming, operating pressure sometimes called burner pressure from test point furthest from incoming on most boiler gas valves.
Tests are usually only possible on hot water mode. Max pressure is confirmed by running bath and basin taps full on, should be 16.3. Min pressure is confirmed by removing one lead of coil on gas valve.
Adjustment is outer nut for max, inner screw for min. Must hold opposite one still while adjusting and recheck one after adjustment of other. Fine tuning via pcb pot on that boiler, but you are far from fine tuning.
I don't know the voltages that this gas valve works on, but set meter on dc volts 250 range. Test at correct two pins of pcb or at end of leed to gas valve. You'd expect changing voltage as you run a tap slow or fast.
By the way, there is a dhw high limit stat so I am conscernmed about the 3 bar pressure, the high limit stat should prevent rediculous levels. I suspect there is also a problem with the expansion vessel. Take off the dust cap depress the pin, if water comes out you need a new one, if air, you need to check the charge pressure, and pump up as required.
I don't know what the performance of this pcb is when an ntc (negative temp coefficient) thermister (resister that varies with temperature) is out of range some won't procced to anything, this one may act bisaarly as your seems to. You need to obtain the temperature resistance chart for the ntc, ask the manufacturer explain your level they may provide it. First and most simply we check the room temperature resistance, if it fails this we change it anyway. Probably the same part for CH side so we swap them over in the first instance to fault fine. Full test involves jug of water thermometer and ohm meter. For most boilers its a very cheap part so we don't quibble and change it anyway. Halstead's it costs £25 so we think twice, but I bet there is an Ariston part which is right.