Well folks, it's that time again!

This week I have a bit of a quiz for you.

Can anyone spot what is very wrong with this installation?


IMGP0914-1.jpg
 
Sponsored Links
no earth to Proteus or Wylex

no main bonding
 
The proteus is actually earthed. The wylex is not.

There is no main bonding

There is another fault IMO worse that this.
 
Lacks a single point of isolation is one obvious fault.

Is the heating CU picking its neutral feed from the Hagar CU?
 
Sponsored Links
there seems to be a red core running from "heating" CU to Hager. What's it for?

the "Heating" connections box looks as if it might be fed from the Hager as well as the "Heating" CU

No main switch

edited: bah!
 
No single point of isolation

BS 951 clamp on incomer

Undersize phase between Hager and Crabtree

Neutral linked between Hager and Crabtree, whereas Phase is not
 
Ricicle wins a gold star :LOL:


The crabtree CU has its live fed direct from the henley block, yet it's neutral is fed from the load side of the hager CU.

Switching off the main switch in the hager CU stops all the heaters in the place, and they appear dead, but they have really just lost their neutral, and really remain live.

Not good.
 
RF Lighting said:
Ricicle wins a gold star :LOL:


The crabtree CU has its live fed direct from the henley block, yet it's neutral is fed from the load side of the hager CU.

I'll have one too if you don't mind. Check the posts above Ricicles ;)
 
You appear have edited your post. I hope there isn't foul play occouring here :eek: :LOL:
 
GaryMo said:
RF Lighting said:
Ricicle wins a gold star :LOL:


The crabtree CU has its live fed direct from the henley block, yet it's neutral is fed from the load side of the hager CU.

I'll have one too if you don't mind. Check the posts above Ricicles ;)

:p :p :p :p
 
Oh ok you can have a gold star too :LOL:

No one spotted the lack of RCD protection ;)


Anyway, its all better now :LOL:

IMGP0955.jpg


(I know it still has BS951 clamps on the incommer :LOL: )
 