The MEM RCD's will trip if the neutral goes open circuit or high resistance.
If your meter is also reporting this type of fault (posh meter - never seen that before), then you can assume you have a neutral fault to your property. Surprised that your supplier didn't send anyone out if that is the message your meter gave?? A lost neutral on a supply is highly dangerous, especially on a PME supply.
RCD's in my experience are more likely to trip due to a fault on any circuit, but a large(ish) overall current draw. Any current inbalance will trip it, and this could be due to a N to E fault any ANY cct on the RCD, or a fault from L to E on an isolated cct due to internal element/load resistance to neutral.
If your meter is also reporting this type of fault (posh meter - never seen that before), then you can assume you have a neutral fault to your property. Surprised that your supplier didn't send anyone out if that is the message your meter gave?? A lost neutral on a supply is highly dangerous, especially on a PME supply.
RCD's in my experience are more likely to trip due to a fault on any circuit, but a large(ish) overall current draw. Any current inbalance will trip it, and this could be due to a N to E fault any ANY cct on the RCD, or a fault from L to E on an isolated cct due to internal element/load resistance to neutral.