Replacing a circuit breaker in MCB

Discussion in 'Electrics UK' started by Tadhg, 23 Sep 2008.

  1. Tadhg

    Joined:
    23 Sep 2008
    Messages:
    4
    Thanks Received:
    0
    Location:
    Berkshire
    Country:
    United Kingdom
    I killed a 30A circuit breaker (MK LN5930) in my MK Sentry consumer unit. Don't ask how - it was silly! It is dedicated to an oven which is in need of repair and now trips the main switch in the consumer unit.

    I have found a replacement MCB and wondering is it easy to replace these?

    The oven is being replaced also. :LOL:
     
  2. jj4091

    Joined:
    1 Dec 2006
    Messages:
    3,384
    Thanks Received:
    230
    Location:
    Cumbria
    Country:
    United Kingdom
    Not being sarcastic but the last time I saw a diy mcb replacement it resulted in the main fuse continually blowing. It was done by someone who assured their friend he knew what he was doing. ;)
     
  3. Steve

    Joined:
    15 Apr 2005
    Messages:
    16,009
    Thanks Received:
    226
    Location:
    Yorkshire
    Country:
    United Kingdom
    Its quite easy. Just be extremely cautious. The main incoming cables to the consumer unit are always live - unless someones fitted an upstream isolator.

    Turn off mainswitch (and isolate elsewhere if you can).

    Test for dead - go round, turn lights on, a radio etc.

    Use your multimeter to test the busbar (via the mcb bottom screws if accessible) for dead. To be sure, turn the lectric back on and retest for live (then you know your multimeter and lights are working) - then back off and retest for dead.

    Now, unscrew the outgoing live wire from the MCB. Then unscrew the bottom screw, which holds the busbar prong. Now, at the back of the MCB is a clip that holds it onto the DIN rail. At the bottom will be a slot to insert a screwdriver and prise downwards. This will release the clip and you can lift the MCB out.

    You may find it a little easier to loosen the busbar from the other MCBs too, since this can hold the MCB in place on its own. I found it easier doing it this way when I changed my Hager MCBs. MK look a similar design.

    To refit, reverse the above!

    Not sure of the legals of this procedure.

    The new oven - what wattage is it?
     
  4. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    52,098
    Thanks Received:
    2,033
    Location:
    London
    Country:
    United Kingdom
    The how is important, as it might have been something that damaged the cable, or caused by a damaged cable


    The RCD trip might be down to a damaged cable...
     
  5. Dartlec

    Joined:
    6 Dec 2006
    Messages:
    127
    Thanks Received:
    0
    Location:
    Kent
    Country:
    United Kingdom
    You don't think we are going to let that go without asking do you? :LOL:

    The replacement wasn't this one was it - dated 1965?!

    Steve gives generally good advice, but I would be very wary of using a second hand mcb and relying on it to still work as promised. (There is no easy way to check an MCB trips at the stated rating).

    When you say the oven now trips the 'main switch' in the CU, I presume you mean you have an RCD incomer? Any chance of a picture?

    Legally, I would say this counts as replacing a damaged component so would not be notifiable under Part P. However, with an older install like yours , an hours worth of a local electrician's time to replace the mcb and at the same time cast an eye over the whole installation may well be money well spent.

    Gavin
     
  6. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    52,098
    Thanks Received:
    2,033
    Location:
    London
    Country:
    United Kingdom
    The same situation faces everyone who buys a house and doesn't replace the CU with a new one...
     
  7. Dartlec

    Joined:
    6 Dec 2006
    Messages:
    127
    Thanks Received:
    0
    Location:
    Kent
    Country:
    United Kingdom
    True, but the mcbs are more likely to have come new from the manufacturer and not in a jiffy bag via the Royal Mail's careful handling...

    And of course the original certificate and 10 yearly PIR documentation will show you the history.... ;) :rolleyes: (When was the last time someone turned up to an install older than 3 years and actually found an installation certificate!)

    Actually, I have no idea what the MCB failure rate is (I know the RCD rate is rather higher than one might think) and I've never seen an instrument designed for testing trip times/ratings, but can't immediately think of a reason why one couldn't be developed for onsite use?

    I'm certainly not saying the OP shouldn't replace the MCB, was just sounding a note of caution.

    Gavin
     
  8. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    52,098
    Thanks Received:
    2,033
    Location:
    London
    Country:
    United Kingdom
    Somebody should make a tester.

    A car battery can easily supply enough current to trip a breaker (in a domestic CU), and at 12V (I'm guessing) there wouldn't be enough energy to damage it.

    You'd need to be able to select the rating and curve, and you would only realistically be able to check the 5xIn/10xIn fast trip time, not I1 or I2, but that would be better than nothing.

    [rummage]Looks for large box, some 10kW rated milli-ohm range resistors (hmmm), storage 'scope[/rummage]

    :D
     
  9. plugwash

    Joined:
    28 Mar 2004
    Messages:
    8,818
    Thanks Received:
    265
    Country:
    United Kingdom
    The problem is the currents involved. RCDs are tested with relatively small currents so they are easy and safe to test.

    MCBs are a whole different ball game. The current needed to test fast trip on a MCB would range from 30A for a B6 to 1260A for a D63 . Such currents could not be safely passed through probes and for the larger breakers could also cause issues on the supply side. And if they are faulty such high currents may cause violent failure.

    IMO the only safe way to test a MCB would be to remove it from the board and place it in a suitable enclosure to resist violent failure, then feed the current to it from a special power supply pack. The power supply pack would need to be able to supply significant voltage as the current dropped off to test the MCBs ability to safely break the arc.
     
  10. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    52,098
    Thanks Received:
    2,033
    Location:
    London
    Country:
    United Kingdom
    You might be able to get this into a van: http://www.eurosmc.com/pdffile/smc-12_i.pdf


    The immediate problem I can see is how would you deliver 315+ amps (assuming a B63 is the largest you'd want to test - it'd be 630A for a C63)?

    It's not so much the power source, more what the internal wiring would be like.

    You can get thyristors to do the switching, but at some point you're going to have to be able to deliver that zap down a couple of cables.

    35mm² tri-rated? Could that handle the current repeatedly, and sufficiently frequently to make the tester of practical use?
     
  11. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    52,098
    Thanks Received:
    2,033
    Location:
    London
    Country:
    United Kingdom
    There are probably some things you'd have to take as read, and that would be one. For a manufacturer to test samples is one thing, but you'd actually want to avoid arcing in something you were going to put back.

    "OK, Mr Jones - your MCBs were all fine - 100% success rate in testing. Of course they're trashed now, but don't worry, I've got new ones in the van." :D

    That tester I linked to above only uses 2.3 - 20.3V....
     
  12. Tadhg

    Joined:
    23 Sep 2008
    Messages:
    4
    Thanks Received:
    0
    Location:
    Berkshire
    Country:
    United Kingdom

    New oven is 6.1kW. Thanks for the detailed response.
     
  13. Tadhg

    Joined:
    23 Sep 2008
    Messages:
    4
    Thanks Received:
    0
    Location:
    Berkshire
    Country:
    United Kingdom
     
  14. RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    18,443
    Thanks Received:
    1,118
    Location:
    Leeds
    Country:
    United Kingdom
    Does the MCB stay up when the main switch is in the OFF position?
     
  15. Dartlec

    Joined:
    6 Dec 2006
    Messages:
    127
    Thanks Received:
    0
    Location:
    Kent
    Country:
    United Kingdom
    After the build up I'm disappointed you couldn't find a more novel way to break it :LOL:

    In that case cable damage is unlikely, so I see no reason why you couldn't tackle the job. Just make sure you have a voltage indicator you know works and ensure everything is isolated!

    Gavin
     