scaled plate exchangers

Joined
3 Aug 2008
Messages
23
Reaction score
0
Location
Cardiff
Country
United Kingdom
could anyone tell me what would be the result of scaled plate exchanger? poor dhw flow, poor h/w temp as there would be karge temp differntial on flow and return? anything else? wouldnt the boiler overheat if the plate was scaled up?thank you
 
Sponsored Links
Poor DHW flow if scaled badly on the domestic side. Most plate HE's tend to block on the system side and cause hot/cold hot/cold cycling as the boiler overheats/cools/overheats.
 
If the plate is scaled then poor hot water heat up or poor flow rates.

If its plate is sludged then fluctuating water temps, poss boiler overheats
 
Sponsored Links
thanks. i guess measuring the temp diff of flow into the plate and return out is confirmation of blockage/scale. should be 10 percent differential?
 
thanks. i guess measuring the temp diff of flow into the plate and return out is confirmation of blockage/scale. should be 10 percent differential?

No, that is on your rads, or flow and return on boiler. Your DHW indication is explained above
 