10mm2 with a 40A MCB behind a 30ma B type RCD.
Personally, I would go with an RCBO.
http://www.gil-lec.co.uk/products/C...MK+RCBO+40a+30mA+17th+Edition+RCBO/3579900800
Max cable length 66 metres for both TN-C-S and TNS Earthing. Good for installation methods A,C,100,102 (Enclosed in conduit in wall, clipped direct, in roof/floor with <100mm insulation, in roof/floor >100mm insulation).
Hope this helps.
You really need to get your leccy to do their sums though. If you end up zapping yourself, its your own fault.
Table C9.2 to "Guide to the Wiring Regulations 17th Edition". Available on the net as an illicit download if you know where to look.