I don't understand the problem you envisage...2 single boxes wouldn't be any good, as I was wanting to feed tails in one end and SWA out the other.
I don't understand the problem you envisage...2 single boxes wouldn't be any good, as I was wanting to feed tails in one end and SWA out the other.
Nope - and I probably never will, even though there are five 800KMFs there in total. However, I suppose that I'm a born pessimist, in that I always try to avoid (sometimes 'cost permitting!) having only a single spare for anything - through fear that, should a spare ever have to be deployed, it might possibly prove faulty and itself fail almost immediately! ... and, of course, if I stored the second spare anywhere other than where you have seen, I would probably never be able to find it 'years down the road' if ever I needed to!Have you ever needed either of them?I've got more than himLove the spare fuse holder
433.2.2
Why not look it up?433.2.2
What's that then?
True, but that's not really the main thing I was thinking of - since I would hopefully identify and remove the fault before subjecting a replacement fault to it!John - a fair point. If one blows a second is likely to if fault is still present.
I would want something metal to allow me to correctly terminate SWA to.
You could probably build something small-ish with 2 1-gang metalclad boxes, one with a switch and one with a panel-mount fuse.
Yep, I presume that's what BAS was getting at. If, as you said, the outgoing cables from the fuse are going to be 1.5mm² or 2.5mm², with a fuse appropriately small to protect that cable, then the regs (I mean BS7671) allow that the incoming cable to the fuse (and switch) need not be any larger in CSA than those outgoing cables. Whether the DNOs see it the same way when the only upstream protection to the cable is their fuse, I don't know, since they work to different regulations.So your point is that I don't need to have tails coming in ? ... I could put smaller diameter wires into a henly I guess.?
OK. Do I take it that you don't have a spare way in your CU for this purpose, or have some reason for not wanting to do it that way (e.g. no non-RCD ways available)?Ok. To complete the story. ... I saw the plastic switch fuse going cheap. I know people liked them on here. And considering buying it, and thought it could be of use for this task (if it ever happened) or something else. It was to power a garage which has 2 light tubes and a 16A radial socket circuit. (no heavy loads) ... I think its about 20m away.
OK. Is the meter cupboard (is it an outside one?) a long way from the CU, then?It would be far from easy to route it to the CU. This leaves connection to either the kitchen ring or the meter cupboard.
Even the kitchen ring wouldn't be tidy.
Your decision, although I agree thatis probably the minimum. As I said, even 2.5mm² is technically pretty marginal, and provides little, if any, 'future proofing'.Thanks for the calculations John. So 2.5mm minimum then.
That is correct.Out of interest, I shouldn't need an RCD to protect the SWA then? Its a PME supply. There is an RCD in the garage.
Wouldn't have to be quite that small...Yep, I presume that's what BAS was getting at. If, as you said, the outgoing cables from the fuse are going to be 1.5mm² or 2.5mm², with a fuse appropriately small to protect that cable, then the regs (I mean BS7671) allow that the incoming cable to the fuse (and switch) need not be any larger in CSA than those outgoing cables. Whether the DNOs see it the same way when the only upstream protection to the cable is their fuse, I don't know, since they work to different regulations.