A bit of advice needed on this, got a customer that's moved into a house with a cowboy installation!
It's a large-ish house with 30 rads over three floors. It's a Glowworm 38HXI on an S-plan, grundfos 15/60 and a 250L unvented cylinder all installed in the cellar. All on plastic 22/15mm (barriered)
Problem i've got is the top floor doesn't heat at all and when the boiler comes on it cycles high/low every few seconds (when I open the bypass it stops cycling and runs ok) I think the pump/pipework is way undersized and can't get rid of the 38KW. Trouble is, I can only touch the plan/boiler pipework as the rest of it is tiled under floors etc.
I was thinking of upgrading the visible pipework and pump and maybe installing some kind of LLH or buffer to help the boiler stop cycling. Keep the 15/60 for the boiler and use a 25/55 for the system.
Would this set-up mean too narrower temp-diff accross the heat ex meaning it wouldn't condense?
Or am I barking up the wrong tree completely! Just trying to avoid telling the guy his expensive floors need to come up!
Thanks
It's a large-ish house with 30 rads over three floors. It's a Glowworm 38HXI on an S-plan, grundfos 15/60 and a 250L unvented cylinder all installed in the cellar. All on plastic 22/15mm (barriered)
Problem i've got is the top floor doesn't heat at all and when the boiler comes on it cycles high/low every few seconds (when I open the bypass it stops cycling and runs ok) I think the pump/pipework is way undersized and can't get rid of the 38KW. Trouble is, I can only touch the plan/boiler pipework as the rest of it is tiled under floors etc.
I was thinking of upgrading the visible pipework and pump and maybe installing some kind of LLH or buffer to help the boiler stop cycling. Keep the 15/60 for the boiler and use a 25/55 for the system.
Would this set-up mean too narrower temp-diff accross the heat ex meaning it wouldn't condense?
Or am I barking up the wrong tree completely! Just trying to avoid telling the guy his expensive floors need to come up!
Thanks