Will cental heating flow though this pipewok ok

Sponsored Links
Be worth putting a manual bleed vent at the highest level for getting air out when initially filling, but a good sealed system will not produce air so once its vented and running then no there would be no problem with that.
 
There is a rad at the top level so should this get all the air out?
 
Yea that would be fine. Probably need to bleed it a few times in the first few weeks then after it should be all good
 
Sponsored Links
Thanks the pipework shown is how the flow exits to boiler to the main run which rads branch off
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top