wiring cm927 to ecotec pro 28

If you look at the two pin plug @ RT 240 on boiler you will see only one terminal is used.

RT 240 to term B of receiver.
Perm live to L of receiver.
Link L to A @ receiver.

The way it's wired at the moment you have no voltage to A due to RT 240 @ boiler being a 'dummy' terminal....In other words NO VOLTAGE.

.........I agree it can be confusing ,we've all done it.:sneaky:

BTW , the right hand terminal @ RT 240 is switched live from stat (B).
 
Sponsored Links
You could always remove link from RT 24 and use these terminals to connect to receiver A B , forget RT 240.
 
Finally got there! cheers!

Removed link from RT 24 connected two wires to RT 24 and linked to receiver A B

Boiler fires up but the temp increases briefly but is not increasing? rad symbol on display is flashing
 
Sponsored Links
Boiler fires up but the temp increases briefly but is not increasing? rad symbol on display is flashing
 