Wiring Help For Wireless Thermostat Honeywell CM927

Joined
30 Aug 2008
Messages
223
Reaction score
3
Country
United Kingdom
Its actually a Homexpert THR872CUK which is the same but different branding. Any help would be appreciated.

The following images:
1. Diagram of upstairs wiring
THR872CUK_zpsf8978c25.jpg

2. Upstairs wiring box
11F4FD91-5F55-41A2-ADB8-5B916863D460-859-0000008C58D31F8C.jpg

3. Close up of above
D4BCB0F0-90E7-4A42-9948-C286CD865E50-859-0000008C643B0C68.jpg

4. Programmer upstairs
2E288213-8438-40BE-AEF4-C763AF9BFD00-859-0000008C6CD72B80.jpg

5. Downstairs wiring (where boiler is located)
9B77794D-6423-443E-BF16-42838020CA46-859-0000008C73E6DCBD.jpg

6. Labeling of above fascia
6A7A6256-97ED-48B5-A8C2-AD06E6E5C55E-859-0000008C7B91172C.jpg

7. Downstairs wiring closeup
DEE40FA0-DDA1-4903-8280-26223AF1311B-859-0000008C81B8001B.jpg

8. Downstairs Bolier pump wiring
A768F8F9-752D-42E9-9779-5443B0D61045-859-0000008C8A7DC8A7.jpg


Programmer/cylinder+stat is located upstairs, the bolier is located downstairs. The 2 port valves and it's additional wiring box is located in the loft.

Central Heating package consists of...
Potterton Kingfisher 2 RS100 Boiler
Open Vented Cylinder (Thermostat) with immersion Heater (Airing Cupboard)
S PLAN
2x Honeywell 2 Port Valves
Honeywell ST6300A Programmer
Fernox TF1
grundfos Alpha Pump
lockshield Valves Honeywell VT117E/VT200 & draytons[/img]
 
Sponsored Links
I have no idea where your cables go - there is no standard colour allocation of cores in heating installations. Even a green could be used as a phase wire.

However, you are in luck because I'm a qualified electrician as well as a Gas Safe dom/com. You can wire your CM927 to the ST timer, or to the other end of cable running to it.

The live and neutral in the ST timer are labelled L & N, run additional cables from here to L and N on the BDR relay box. You then take the cable out of pin 4 in the ST timer, and wire it to B in the BDR. Run a new wire from BDR terminal A to the ST timer terminal 4.

Job done.

Ps: stay away from Ebay, there is a dodgy batch of CM units out there where the displays conk out. Honeywell took some back from the merchants.
 
I have no idea where your cables go - there is no standard colour allocation of cores in heating installations. Even a green could be used as a phase wire.

However, you are in luck because I'm a qualified electrician as well as a Gas Safe dom/com. You can wire your CM927 to the ST timer, or to the other end of cable running to it.

The live and neutral in the ST timer are labelled L & N, run additional cables from here to L and N on the BDR relay box. You then take the cable out of pin 4 in the ST timer, and wire it to B in the BDR. Run a new wire from BDR terminal A to the ST timer terminal 4.

Job done.

Ps: stay away from Ebay, there is a dodgy batch of CM units out there where the displays conk out. Honeywell took some back from the merchants.

Simond you are 5*****! Just wired it up and testing it as I type. All looks well. :) I bought the Homexpert THR872CUK from Amazon (wanted warranty/amazon service), its very similar to the CM927. Although with this model the front flap comes off and with the CM927 it folds up, minor gripe...

Thanks again for your help/input.
Sparky
 