boiler operating pressure measurement, ideal boiler.


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
cascas

from United Kingdom

Joined: 10 May 2011
Posts: 89
Location: West Midlands,
United Kingdom
Thanked: 1 time

PostPosted: Fri Feb 24, 2012 11:53 pm Reply with quote

On a ideal logic boiler, as far as I know there is only one test point for gas pressure on the incoming isolation valve/integral testpoint.

Operating pressure is showing as 18mbar which seems a little low. The manual states that The external gas cock could further reduce the operating pressure when measured at its test point. The pressure drop is relative to the heat input to the boiler (kW) (approx 1.5mbar),

I have come across WB boilers where there is a pressure drop between the isolation valve and the gas valve, but cannot see how the boiler could affect the measurement at the isolation valve. Has anyone else got experience of these ideal boilers?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
gaswizzard

from United Kingdom

Joined: 08 Oct 2011
Posts: 6277
Location: Hertfordshire,
United Kingdom
Thanked: 986 times

PostPosted: Sat Feb 25, 2012 12:47 am Reply with quote

Are you referring to a premix burner? (zero governor)
Back to top
 Alert Moderators
cascas

from United Kingdom

Joined: 10 May 2011
Posts: 89
Location: West Midlands,
United Kingdom
Thanked: 1 time

PostPosted: Sat Feb 25, 2012 1:01 am Reply with quote

gaswizzard wrote:
Are you referring to a premix burner? (zero governor)


yes.
Back to top
 Alert Moderators
gaswizzard

from United Kingdom

Joined: 08 Oct 2011
Posts: 6277
Location: Hertfordshire,
United Kingdom
Thanked: 986 times

PostPosted: Sat Feb 25, 2012 1:07 am Reply with quote

cascas wrote:


I have come across WB boilers where there is a pressure drop between the isolation valve and the gas valve?


Not uncommon to see a pressure drop between isolation valve and inlet pressure test point on gas valve , if a premix then you will see a negative pressure reading at burner pressure test point.
Back to top
 Alert Moderators
cascas

from United Kingdom

Joined: 10 May 2011
Posts: 89
Location: West Midlands,
United Kingdom
Thanked: 1 time

PostPosted: Sat Feb 25, 2012 6:30 pm Reply with quote

I refer to the Ideal Independent (logic) rated at 33.7kw gross (30.4 nett)

The working pressure at the meter is 21mbar, and at the test point on the boiler 18mbar

I have gas rated the boiler and obtained a measurement of 2.91m3/hr. The MI show a gas rate of 3.13m3/hr (based on a cv of 38.7), so around 7% below MI. If adjusted for CV that the expected gas rate is around 3.03 or the achieved rate is approx. 4% below theoretical. Both within a tolerance -10% / +5%

Without fitting a test point on the pipework, it not possible to confirm pressure loss over the pipework,

Is the supply undersized as I suspect, or does the inlet test point on the ideals give a low reading. (it shouldnt as it on on the isolation cock, rather than the gas valve)?


Last edited by cascas on Sun Feb 26, 2012 8:29 am, edited 1 time in total
Back to top
 Alert Moderators
simond

from United Kingdom

Joined: 26 Oct 2004
Posts: 4066
Location: Surrey,
United Kingdom
Thanked: 272 times

PostPosted: Sat Feb 25, 2012 8:41 pm Reply with quote

Are you a registered installer?

Do you have a combustion analyser, use of this may enable you to adjust the boiler to give the correct gas rate.
Back to top
 Alert Moderators
gaswizzard

from United Kingdom

Joined: 08 Oct 2011
Posts: 6277
Location: Hertfordshire,
United Kingdom
Thanked: 986 times

PostPosted: Sat Feb 25, 2012 9:40 pm Reply with quote

Exactly , burner maybe running a tad lean , CO2% maybe a tad low hence the lean burn , unless you know how to use a FGA and interpret the ersults then you're p**sing in the wind.
Back to top
 Alert Moderators
gaswizzard

from United Kingdom

Joined: 08 Oct 2011
Posts: 6277
Location: Hertfordshire,
United Kingdom
Thanked: 986 times

PostPosted: Sat Feb 25, 2012 9:49 pm Reply with quote

cascas wrote:


I have gas rated the boiler and obtained a measurement of 2.91m3/hr. The MI show a gas rate of 3.13m3/hr (based on a cv of 38.7), so around 7% below MI. If adjusted for CV that the expected gas rate is around 3.03 or the achieved rate is approx. 4% below theoretical. Both within a tolerance -10% / +5%


Based on a CV of 38.7 and a gas rate of 2.91 m3/h gross input would be around 31.12 kw/hr , 3.13m3/hr would be around 33.64 kw/hr.
Back to top
 Alert Moderators
shambolic

from United Kingdom

Joined: 25 Aug 2008
Posts: 1402
Location: United Kingdom
Thanked: 355 times

PostPosted: Sun Feb 26, 2012 5:01 pm Reply with quote

Take the screw right out as reading can be low due to this. Also check pipe size and run. As for co2 readings etc you can't and must not attempt to adjust as gas valve is fixed.
Back to top
 Alert Moderators
patsmotors

from United Kingdom

Joined: 11 Jan 2012
Posts: 53
Location: Middlesex,
United Kingdom
Thanked: 5 times

PostPosted: Sun Feb 26, 2012 6:38 pm Reply with quote

where is Agile,you can never find an Agile when you need one.

Combustion chamber question,i think.
Back to top
 Alert Moderators
gaswizzard

from United Kingdom

Joined: 08 Oct 2011
Posts: 6277
Location: Hertfordshire,
United Kingdom
Thanked: 986 times

PostPosted: Sun Feb 26, 2012 7:22 pm Reply with quote

patsmotors wrote:
where is Agile,you can never find an Agile when you need one.

Combustion chamber question,i think.


Why is that? , nothing has been said that isn't in the MIs , considering the MIs are left with the end user then no problem. icon_confused.gif
Back to top
 Alert Moderators
patsmotors

from United Kingdom

Joined: 11 Jan 2012
Posts: 53
Location: Middlesex,
United Kingdom
Thanked: 5 times

PostPosted: Sun Feb 26, 2012 7:59 pm Reply with quote

Agile knows best.


Last edited by patsmotors on Sun Feb 26, 2012 9:17 pm, edited 1 time in total
Back to top
 Alert Moderators
gaswizzard

from United Kingdom

Joined: 08 Oct 2011
Posts: 6277
Location: Hertfordshire,
United Kingdom
Thanked: 986 times

PostPosted: Sun Feb 26, 2012 9:10 pm Reply with quote

Again what's your point? icon_rolleyes.gif
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Gas flow rate measurement 5 100 Tue Dec 06, 2011 10:22 pm
High Boiler operating Pressure - Alpha CB24 3 1960 Mon Dec 03, 2007 9:52 pm
Operating pressure question 21 340 Sun Jul 06, 2014 2:30 pm
Working,standing,operating,inlet and burner pressure? 5 7180 Sun Feb 21, 2010 10:56 am
Obtaining operating manual for old Myson boiler. 5 3160 Sun Sep 11, 2005 9:14 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.