But Ban likes arguing semantics, so let's go for it!
True - but I think I'll leave that to you, should you feel that it's worth pursuingBut Ban likes arguing semantics, so let's go for it!
As for the 2nd one - you frequently point out that DNOs do not work to BS 7671.I think that you had better inform all the caravan sites in the UK that limit hook-up loads that way and all the DNOs that use fuses for the same use. To name just two applications.
No, because that should not be used if the load is going to be greater than 13A, and it should not be used in order to ensure that a load (not a fault) of >13A gets disconnected.Surely using an FCU with a 13A fuse to feed sockets is doing just that as well
No, it comes down to what 433.1.1 says, not to a study of meaning.Indeed, and I think this essentially comes down to fairly pedantic semantics.
As I recently wrote, is that not one of the ways in which the 13A fuse prevents the cable being overloaded? Whilst one should not design, say, a fused spur from a ring final for a load which one thinks is 'likely to' exceed 13A, the designer obviously has no way of ensuring that loads totalling >13A will never be plugged into the sockets, so the fuse serves to protect the cable should that (deemed 'unlikley') situation ever arise.No, because that should not be used if the load is going to be greater than 13A, and it should not be used in order to ensure that a load (not a fault) of >13A gets disconnected.Surely using an FCU with a 13A fuse to feed sockets is doing just that as well
433.1.1 merely says that the design current of a circuit should not exceed the In of the OPD. As I've just written, in the absence of a crystal ball, a designer who bases his/her design current on the belief that the current 'is not likely' to exceed In (13A fuse in the case under discussion) can (in the case of a sockets circuit) never be certain that this load will never be exceeded - hence the OPD will operate if that 'unlikely' scenario comes to pass.No, it comes down to what 433.1.1 says, not to a study of meaning.Indeed, and I think this essentially comes down to fairly pedantic semantics.
As you say, the OP's 10A radial circuit is not A1, A2 or A3, but it appears to me to have been designed appropriately:If he is not confident then a 13A fused spur is clearly an inappropriate design. Yes, of course a socket circuit has uncertainties, but in this case the OP has not designed a standard A1/A2/A3 circuit - he has struck out anew and created a new design.
Indeed not, but that's not what the OP did. He estimated Ib as 7.9A ("certainly less than 10A") and took a view (I suspect conservative) that Iz was 13.5A, and on that basis selected In as 10A. Provided one accepts his estimate of Ib, then that sounds like a totally correct design process, doesn't it?Ib ≤ In ≤ Iz
You do not chose the value of In as a way to limit Ib.
The reason for the 10A MCB is to protect the cable from overheating due to the insulation.
You don't seem able to let go of the fact that, in what you've quoted above, the OP probably chose less than ideal language. I suggest that you consider everything he has written, rather than focussing on one sentence. As I wrote:No, it doesn't:The reason for the 10A MCB is to protect the cable from overheating due to the insulation.
If one accepts that the MCB is there to provide both overload and fault protection, and if one takes the OP's phrase "to protect the cable due to overheating because of the installation" to mean "to protect from overload a cable whose Iz has been reduced to 13.5A because of insulation", then I don't think that any reasonable person would have a problem with the statement.I think the OP understands that, but perhaps didn't choose his words all that well. He estimates the load as "always under 10A" and, if you read what he's written, he selected the 10A MCB to protect the cable on the basis of a (I think pretty pessimistic) assumption of a CCC of only 13.5A.
So would I, but the OP seems pretty adamant that he would 'never' want more than 10A.If it was me I would be putting a cable in that would allow me to plug in a 13A appliance like an electric heater. Doing otherwise seems short sighted.