Replacing a circuit breaker in MCB

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
Tadhg

from United Kingdom

Joined: 23 Sep 2008
Posts: 4
Location: Berkshire,
United Kingdom

PostPosted: Tue Sep 23, 2008 4:33 pm Reply with quote

I killed a 30A circuit breaker (MK LN5930) in my MK Sentry consumer unit. Don't ask how - it was silly! It is dedicated to an oven which is in need of repair and now trips the main switch in the consumer unit.

I have found a replacement MCB and wondering is it easy to replace these?

The oven is being replaced also. icon_lol.gif
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
jj4091

from United Kingdom

Joined: 01 Dec 2006
Posts: 3040
Location: Cumbria,
United Kingdom
Thanked: 179 times

PostPosted: Tue Sep 23, 2008 5:16 pm Reply with quote

Not being sarcastic but the last time I saw a diy mcb replacement it resulted in the main fuse continually blowing. It was done by someone who assured their friend he knew what he was doing. icon_wink.gif
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 15934
Location: Yorkshire,
United Kingdom
Thanked: 221 times

PostPosted: Tue Sep 23, 2008 5:46 pm Reply with quote

Its quite easy. Just be extremely cautious. The main incoming cables to the consumer unit are always live - unless someones fitted an upstream isolator.

Turn off mainswitch (and isolate elsewhere if you can).

Test for dead - go round, turn lights on, a radio etc.

Use your multimeter to test the busbar (via the mcb bottom screws if accessible) for dead. To be sure, turn the lectric back on and retest for live (then you know your multimeter and lights are working) - then back off and retest for dead.

Now, unscrew the outgoing live wire from the MCB. Then unscrew the bottom screw, which holds the busbar prong. Now, at the back of the MCB is a clip that holds it onto the DIN rail. At the bottom will be a slot to insert a screwdriver and prise downwards. This will release the clip and you can lift the MCB out.

You may find it a little easier to loosen the busbar from the other MCBs too, since this can hold the MCB in place on its own. I found it easier doing it this way when I changed my Hager MCBs. MK look a similar design.

To refit, reverse the above!

Not sure of the legals of this procedure.

The new oven - what wattage is it?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47189
Location: London,
United Kingdom
Thanked: 1719 times

PostPosted: Tue Sep 23, 2008 6:40 pm Reply with quote

Tadhg wrote:
I killed a 30A circuit breaker (MK LN5930) in my MK Sentry consumer unit. Don't ask how - it was silly!

The how is important, as it might have been something that damaged the cable, or caused by a damaged cable


Quote:
It is dedicated to an oven which is in need of repair and now trips the main switch in the consumer unit.

The RCD trip might be down to a damaged cable...
Back to top
 Alert Moderators
Dartlec

from United Kingdom

Joined: 06 Dec 2006
Posts: 127
Location: Kent,
United Kingdom

PostPosted: Tue Sep 23, 2008 6:46 pm Reply with quote

Tadhg wrote:
I killed a 30A circuit breaker ......Don't ask how - it was silly!


You don't think we are going to let that go without asking do you? icon_lol.gif

The replacement wasn't this one was it - dated 1965?!

Steve gives generally good advice, but I would be very wary of using a second hand mcb and relying on it to still work as promised. (There is no easy way to check an MCB trips at the stated rating).

When you say the oven now trips the 'main switch' in the CU, I presume you mean you have an RCD incomer? Any chance of a picture?

Legally, I would say this counts as replacing a damaged component so would not be notifiable under Part P. However, with an older install like yours , an hours worth of a local electrician's time to replace the mcb and at the same time cast an eye over the whole installation may well be money well spent.

Gavin
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47189
Location: London,
United Kingdom
Thanked: 1719 times

PostPosted: Tue Sep 23, 2008 6:55 pm Reply with quote

Dartlec wrote:
I would be very wary of using a second hand mcb and relying on it to still work as promised. (There is no easy way to check an MCB trips at the stated rating).

The same situation faces everyone who buys a house and doesn't replace the CU with a new one...
Back to top
 Alert Moderators
Dartlec

from United Kingdom

Joined: 06 Dec 2006
Posts: 127
Location: Kent,
United Kingdom

PostPosted: Tue Sep 23, 2008 7:10 pm Reply with quote

ban-all-sheds wrote:

The same situation faces everyone who buys a house and doesn't replace the CU with a new one...


True, but the mcbs are more likely to have come new from the manufacturer and not in a jiffy bag via the Royal Mail's careful handling...

And of course the original certificate and 10 yearly PIR documentation will show you the history.... icon_wink.gif icon_rolleyes.gif (When was the last time someone turned up to an install older than 3 years and actually found an installation certificate!)

Actually, I have no idea what the MCB failure rate is (I know the RCD rate is rather higher than one might think) and I've never seen an instrument designed for testing trip times/ratings, but can't immediately think of a reason why one couldn't be developed for onsite use?

I'm certainly not saying the OP shouldn't replace the MCB, was just sounding a note of caution.

Gavin
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47189
Location: London,
United Kingdom
Thanked: 1719 times

PostPosted: Tue Sep 23, 2008 7:11 pm Reply with quote

Dartlec wrote:
(There is no easy way to check an MCB trips at the stated rating).

Somebody should make a tester.

A car battery can easily supply enough current to trip a breaker (in a domestic CU), and at 12V (I'm guessing) there wouldn't be enough energy to damage it.

You'd need to be able to select the rating and curve, and you would only realistically be able to check the 5xIn/10xIn fast trip time, not I1 or I2, but that would be better than nothing.

[rummage]Looks for large box, some 10kW rated milli-ohm range resistors (hmmm), storage 'scope[/rummage]

icon_biggrin.gif
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 8516
Location: United Kingdom
Thanked: 218 times

PostPosted: Tue Sep 23, 2008 7:22 pm Reply with quote

Dartlec wrote:

Actually, I have no idea what the MCB failure rate is (I know the RCD rate is rather higher than one might think) and I've never seen an instrument designed for testing trip times/ratings, but can't immediately think of a reason why one couldn't be developed for onsite use?

The problem is the currents involved. RCDs are tested with relatively small currents so they are easy and safe to test.

MCBs are a whole different ball game. The current needed to test fast trip on a MCB would range from 30A for a B6 to 1260A for a D63 . Such currents could not be safely passed through probes and for the larger breakers could also cause issues on the supply side. And if they are faulty such high currents may cause violent failure.

IMO the only safe way to test a MCB would be to remove it from the board and place it in a suitable enclosure to resist violent failure, then feed the current to it from a special power supply pack. The power supply pack would need to be able to supply significant voltage as the current dropped off to test the MCBs ability to safely break the arc.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47189
Location: London,
United Kingdom
Thanked: 1719 times

PostPosted: Tue Sep 23, 2008 7:30 pm Reply with quote

Dartlec wrote:
I've never seen an instrument designed for testing trip times/ratings, but can't immediately think of a reason why one couldn't be developed for onsite use?


You might be able to get this into a van: http://www.eurosmc.com/pdffile/smc-12_i.pdf


The immediate problem I can see is how would you deliver 315+ amps (assuming a B63 is the largest you'd want to test - it'd be 630A for a C63)?

It's not so much the power source, more what the internal wiring would be like.

You can get thyristors to do the switching, but at some point you're going to have to be able to deliver that zap down a couple of cables.

35mm˛ tri-rated? Could that handle the current repeatedly, and sufficiently frequently to make the tester of practical use?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47189
Location: London,
United Kingdom
Thanked: 1719 times

PostPosted: Tue Sep 23, 2008 7:36 pm Reply with quote

plugwash wrote:
The power supply pack would need to be able to supply significant voltage as the current dropped off to test the MCBs ability to safely break the arc.

There are probably some things you'd have to take as read, and that would be one. For a manufacturer to test samples is one thing, but you'd actually want to avoid arcing in something you were going to put back.

"OK, Mr Jones - your MCBs were all fine - 100% success rate in testing. Of course they're trashed now, but don't worry, I've got new ones in the van." icon_biggrin.gif

That tester I linked to above only uses 2.3 - 20.3V....
Back to top
 Alert Moderators
Tadhg

from United Kingdom

Joined: 23 Sep 2008
Posts: 4
Location: Berkshire,
United Kingdom

PostPosted: Tue Sep 23, 2008 7:55 pm Reply with quote

Steve wrote:

The new oven - what wattage is it?



New oven is 6.1kW. Thanks for the detailed response.
Back to top
 Alert Moderators
Tadhg

from United Kingdom

Joined: 23 Sep 2008
Posts: 4
Location: Berkshire,
United Kingdom

PostPosted: Tue Sep 23, 2008 7:58 pm Reply with quote

[quote="Dartlec";p="1010112"]
You don't think we are going to let that go without asking do you? icon_lol.gif

The replacement wasn't this one was it - dated 1965?!


No, I didn't think I would get away without somebody asking! It was as silly as forcing the switch on with the main switch on. Don't faint!

The replacement is still being sourced, but not the dated one you listed here.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 17439
Location: Leeds,
United Kingdom
Thanked: 933 times

PostPosted: Tue Sep 23, 2008 8:03 pm Reply with quote

Does the MCB stay up when the main switch is in the OFF position?
Back to top
 Alert Moderators
Dartlec

from United Kingdom

Joined: 06 Dec 2006
Posts: 127
Location: Kent,
United Kingdom

PostPosted: Tue Sep 23, 2008 8:05 pm Reply with quote

Tadhg wrote:

No, I didn't think I would get away without somebody asking! It was as silly as forcing the switch on with the main switch on. Don't faint!

The replacement is still being sourced, but not the dated one you listed here.


After the build up I'm disappointed you couldn't find a more novel way to break it icon_lol.gif

In that case cable damage is unlikely, so I see no reason why you couldn't tackle the job. Just make sure you have a voltage indicator you know works and ensure everything is isolated!

Gavin
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Adding an additional Circuit breaker 9 780 Sat Aug 25, 2007 3:20 pm
Circuit Breaker on Neutral 2 400 Thu Sep 06, 2007 1:11 pm
Is it possible to blow a circuit breaker 3 480 Fri Sep 28, 2007 8:22 am
Help with ? broken Electric Shower / circuit breaker trippin 9 4100 Tue Apr 03, 2007 9:01 am
quick circuit breaker question 6 540 Sat Mar 17, 2007 2:16 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.