8.5 kw shower cable size

Goto page Previous  1, 2, 3  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
TopTrumper

from United Kingdom

Joined: 18 Nov 2005
Posts: 282
Location: United Kingdom
Thanked: 1 time

PostPosted: Sat Nov 15, 2008 9:53 pm Reply with quote

GaryMo wrote:
They would need to take my professional advice.
I would recommend an alternative route thus avoiding insulation. If that's not possible then I would inform them that I could install a 10mm cable but it's only rated at 36A and can only supply a shower rated at a maximum of 8kW.

I would NOT install a shower with a rating higher than the current carrying capacity of a cable.

Why is this so difficult to understand? It's like asking me to put a square peg in a round hole - something has to give.


I understand.
Completely. icon_rolleyes.gif
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 4111
Location: Manchester,
United Kingdom
Thanked: 165 times

PostPosted: Sat Nov 15, 2008 9:56 pm Reply with quote

Why the rolling eyes then?
Seriously, is there something you don't understand or don't agree with?
Back to top
 Alert Moderators
equitum

from United Kingdom

Joined: 26 Sep 2006
Posts: 361
Location: Coventry,
United Kingdom

PostPosted: Sat Nov 15, 2008 10:47 pm Reply with quote

TopTrumper wrote:
GaryMo, fair enough, point taken.
Answer me one question, if the OP had said he wanted to install this shower, what cable would you advise him for the 3 metre run?

http://www.alertelectrical.com/Electric-Power-And-Mixer-Showers/Mira-Showers/Mira-Electric-Showers/Mira-Vie-108kw-Electric-Shower-Satin-Chrome-D62127.asp


From the MI.....

"
The electrical installation must comply with the “Requirements for Electrical Installations” (commonly referred to as the IEE Wiring Regulations), or any particular regulations and practices, specified by the local electricity supply company in force at the time of installation. The installation should be carried out by an electrician or contractor who is registered, or is a member of, an association such as:
National Inspection Council for Electrical Installation and Contracting (NICEIC), throughout the UK
The Electrical Contractors Association (ECA), England and Wales
The Electrical Contractors Association of Scotland (ECAS)
"

Personally I would have advised the OP that if he doesn't know what cable size to use he/she is not competent to install it, and its not a suitable DIY job. It strikes me odd that the OP is aware of the thermal insulation derating issue as most "laymen" would not consider it.. icon_confused.gif
Back to top
 Alert Moderators
TopTrumper

from United Kingdom

Joined: 18 Nov 2005
Posts: 282
Location: United Kingdom
Thanked: 1 time

PostPosted: Sat Nov 15, 2008 11:04 pm Reply with quote

GaryMo wrote:
Why the rolling eyes then?
Seriously, is there something you don't understand or don't agree with?


It means you just made yourself look like a right soft c*nt
Back to top
 Alert Moderators
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 4111
Location: Manchester,
United Kingdom
Thanked: 165 times

PostPosted: Sat Nov 15, 2008 11:07 pm Reply with quote

Very classy icon_cool.gif
Back to top
 Alert Moderators
equitum

from United Kingdom

Joined: 26 Sep 2006
Posts: 361
Location: Coventry,
United Kingdom

PostPosted: Sat Nov 15, 2008 11:07 pm Reply with quote

Errrr....toptrumper, I have never known a name so apt as yours, well done !!

EDIT: Please explain why you are not ashamed of giving advice that could potentially cause a fire and at best is contrary to any reg since about the 2nd edition without having a rethink and perhaps an admission you were wrong ?


Last edited by equitum on Sat Nov 15, 2008 11:12 pm, edited 1 time in total
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 17418
Location: Leeds,
United Kingdom
Thanked: 927 times

PostPosted: Sat Nov 15, 2008 11:10 pm Reply with quote

GaryMo wrote:
Very classy icon_cool.gif


Well personal insults are all he can resort to to try and make you look foolish, as your advice about cables in insulation can't be disputed, what with it being right and all.
Back to top
 Alert Moderators
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 4111
Location: Manchester,
United Kingdom
Thanked: 165 times

PostPosted: Sat Nov 15, 2008 11:12 pm Reply with quote

Hence I'm not biting, it's not worth the effort.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 24994
Location: Cheshire,
United Kingdom
Thanked: 426 times

PostPosted: Sat Nov 15, 2008 11:18 pm Reply with quote

I too am puzzled.

Can you please tell me what you would do in the scenario you have described and your reasons for doing so.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47057
Location: London,
United Kingdom
Thanked: 1709 times

PostPosted: Sun Nov 16, 2008 1:02 am Reply with quote

Back to top
 Alert Moderators
NotHimAgain

from United Kingdom

Joined: 08 Feb 2008
Posts: 435
Location: United Kingdom
Thanked: 19 times

PostPosted: Sun Nov 16, 2008 7:14 am Reply with quote

Do nothing - oh that won't do will it - after all there are loads of solutions.

Start by reading 523.7 - in particular the second and third paragraphs. Note to that the cyclic nature of the load maybe taken into account (para 1).

So you could select a different installation method (in the literal sense) and use something other than 70 degree C PVC.
Just pick you cable and de-rate it by 50% - XLPE perhaps or bare MI maybe, the list goes on.

You could also consider using cables of different sizes to cope with the restrictions on heat loss in the loft.

No doubt someone will mention heat transfered via connections, and the problems of actually making those connections but these things can all be solved.

Next icon_biggrin.gif
Back to top
 Alert Moderators
hairyben

from Morocco

Joined: 06 Oct 2008
Posts: 644
Location: Morocco

PostPosted: Sun Nov 16, 2008 10:47 am Reply with quote

10,800 / 240 = 45

Using parallel runs of 6mm will allow 45A+ with any of the new 10X methods.

Or parallel 4mm, wap some trunking round it in the wall and call it ref method A, 26A x2.

Not the norm in domestic and never done it this way myself, but heard it discussed, any thoughts?

cos showers are getting more and more power hungry and people are stuffing insulation everywhere. Gone are the days when people would be overjoyed with a 7.2 mira supreme, and they wonder why their electric bills hit the roof.
Back to top
 Alert Moderators
tSpark

from United Kingdom

Joined: 22 Oct 2008
Posts: 75
Location: Lancashire,
United Kingdom
Thanked: 1 time

PostPosted: Sun Nov 16, 2008 1:07 pm Reply with quote

Had to fit a similar size shower before, that too would only take 10mm. I needed to get through insulation to get across to bathroom roofspace, so I ran 16mm to the shower pullswitch and then the short distance from pullswitch (i kept battened above insulation) to the shower in 10mm,
Back to top
 Alert Moderators
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 4111
Location: Manchester,
United Kingdom
Thanked: 165 times

PostPosted: Sun Nov 16, 2008 1:17 pm Reply with quote

Nothing at all wrong with that.

How did you find terminating a 16mm and 10mm in a pull switch? I'm normally tearing my hair out when connecting 2 x 10mm cables even with the deepest backbox I can lay my hands on!

In fact, I hate pull switches icon_evil.gif
Back to top
 Alert Moderators
tSpark

from United Kingdom

Joined: 22 Oct 2008
Posts: 75
Location: Lancashire,
United Kingdom
Thanked: 1 time

PostPosted: Sun Nov 16, 2008 1:24 pm Reply with quote

I'm getting wise, I wont tackle something like that without having at least one spare patress box at hand, two, if i know im in that short tempered mood icon_evil.gif

Pull switchs are great for one thing, loose terminals, hot contacts and replacement!! (ok three)
Top of the list of things I hate doing at the top of a ladder!
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page Previous  1, 2, 3  Next
Page 2 of 3

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Wot size cable for a 10.5kw electric shower? 9 24240 Fri Apr 08, 2005 12:07 pm
cable size for 10.5kw electric shower 4 960 Thu Mar 25, 2010 12:34 am
Shower size for 6mm cable? 15 2980 Thu Mar 20, 2008 8:11 pm
Shower cable size question 21 1680 Thu Jan 18, 2007 6:04 pm
10.5 kw shower cable size 4 480 Mon Mar 29, 2010 6:16 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.