Hi i recently bought a broag remeha avanta 35c bolier and have just had a plumber round for a quote to install ..

He has advised i get a bigger gas supply pipe of 28mm from the meter to the boiler cupboard which i currently have 22mm pipework... The meter is approximately 10m from from where the current boiler is situated... Obviously this is going to involve more labour and materials with ripping up the floor etc to make good the upgrade..

He says i neeed a bigger supply because the boiler is a 35kw and also because im running a gas hob with single gas oven too...

Can someone please confirm this to be true or is the 22mm pipework i already have adequate to do the job as i had another quote from a heating engineer and he did not mention the pipe upgrade needing to be done...


Thanks in advance Gavin
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
keighern

from United Kingdom

Joined: 08 Jun 2009
Posts: 66
Location: Manchester,
United Kingdom
Thanked: 1 time

PostPosted: Tue May 04, 2010 9:57 pm Reply with quote

depends on number of factures. Needs correct pipe sizing calculations doing to ensure sufficient flow of gas to appliances. To answer your question all installs are different so no definitive answer unless viewed and calculated.
Back to top
 Alert Moderators
greemyamochop

from United Kingdom

Joined: 01 May 2010
Posts: 207
Location: Powys,
United Kingdom
Thanked: 22 times

PostPosted: Tue May 04, 2010 10:32 pm Reply with quote

Maybe that the second engineer is not as good as your first but either way the only way to be sure is by doing correct calculations with the consumption required for all appliances.

When its worked out properly it may mean that only some of the pipework needs to be altered but i would say there is a decent possiblity it needs upgrading.

Mention it to the second engineer, if hes a decent installer hell do the calculations for you, i would if it meant getting the job!!
Back to top
 Alert Moderators
newgas

from United Kingdom

Joined: 12 Oct 2007
Posts: 6103
Location: Lancashire,
United Kingdom
Thanked: 354 times

PostPosted: Tue May 04, 2010 10:36 pm Reply with quote

22mm at 10 mtrs with a hob and gas oven on might be OK but in winter say when the demand is high for heating and you are using both hob and oven with the heating on then the gas pressure is reduced to all appliances because it might not be sufficient for max usage.

That is what you have to work out the MAX usage of appliances and the the size / length of pipe will tell you what the pressure loss will be.

Undersized pipework can cause problems in your appliances and they can potentially become dangerous.

Your plumber could just put in a couple of lengths of 28mm from the meter to the 22mm and that should be OK but I'm going with what youve said, but then I'm not there. icon_rolleyes.gif
Back to top
 Alert Moderators
mickyg

from United Kingdom

Joined: 24 Aug 2005
Posts: 15949
Location: Hertfordshire,
United Kingdom
Thanked: 3200 times

PostPosted: Tue May 04, 2010 11:14 pm Reply with quote

but 10m plus elbows/tees an oven and hob sounds like a 28mm jobby to me. Some modern 5 burner hobs are as much as 12kw, add your oven and your easily in 28mm territory.

if you can get your head around it, you can calculate it using this guide. you will need to know the "input"of each appliance being installed.

http://www.ukcopperboard.co.uk/literature/pdfs/Installation-Tips/Domestic-gas-planning-and-sizing.pdf
Back to top
The following user says thank you to mickyg for this useful post:
westeleven (5 May 2010)
 Alert Moderators
gavm

from United Kingdom

Joined: 04 May 2010
Posts: 2
Location: Devon,
United Kingdom

PostPosted: Wed May 05, 2010 5:43 am Reply with quote

Thanks very much guys for all your input..

After reading your comments i am leaning towards the 28mm having to be used now.

Cheers Gavin
Back to top
 Alert Moderators
newgas

from United Kingdom

Joined: 12 Oct 2007
Posts: 6103
Location: Lancashire,
United Kingdom
Thanked: 354 times

PostPosted: Wed May 05, 2010 5:40 pm Reply with quote

Good choice mate. icon_wink.gif
Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 4966
Location: Suffolk,
United Kingdom
Thanked: 936 times

PostPosted: Wed May 05, 2010 6:21 pm Reply with quote

unless the boiler is VERY close to the gas meter a 28mm supply will nearly always be required IMHO icon_wink.gif
Back to top
 Alert Moderators
Happyplumber

from United Kingdom

Joined: 09 Feb 2009
Posts: 2890
Location: Berkshire,
United Kingdom
Thanked: 674 times

PostPosted: Wed May 05, 2010 6:23 pm Reply with quote

pipe sizeing is critical to any band A boiler so its good idea to do a proper calculation and make sure its the correct size


A big one will be better then a small one icon_biggrin.gif icon_biggrin.gif
Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 4966
Location: Suffolk,
United Kingdom
Thanked: 936 times

PostPosted: Wed May 05, 2010 8:16 pm Reply with quote

Thats what my missus says icon_confused.gif
signed Little John
Back to top
 Alert Moderators
dreadnoughtheating

from United Kingdom

Joined: 31 May 2009
Posts: 2006
Location: Norfolk,
United Kingdom
Thanked: 301 times

PostPosted: Fri May 07, 2010 7:55 pm Reply with quote

And yet again (I say this to the regular CC guys answering this thread - you know who we are...) we have the customer supplying the appliance, and querying the technical knowledge of his installer..... should we as GasSafe installers presumably with a living to make, be answering any such queries?

Answer on a ping-pong ball please

DH
Back to top
 Alert Moderators
ianniann

from United Kingdom

Joined: 22 Mar 2009
Posts: 535
Location: Manchester,
United Kingdom
Thanked: 74 times

PostPosted: Fri May 07, 2010 8:34 pm Reply with quote

Quote:
should we as GasSafe installers presumably with a living to make, be answering any such queries?

No way! Meet in secret under a full moon, ban those NVQs that any fool can study for, and only let the first born son of seven generations of gas fitters apply to Gas Safe icon_wink.gif
Back to top
 Alert Moderators
simond

from United Kingdom

Joined: 26 Oct 2004
Posts: 4071
Location: Surrey,
United Kingdom
Thanked: 273 times

PostPosted: Fri May 07, 2010 8:50 pm Reply with quote

I don't think there is a problem with helping people with a question, whether it is gas related or not.

However I would question the wisdom of the OP buying the boiler and then trying to get someone to fit it.

Very few dedicated installers (eg: individuals/companies who specialize in boiler fitting) will entertain fitting a customer supplied boiler. I get calls regularly from people who are getting quite desparate having bought a boiler on the internet and can't find anyone prepared to fit it.

If you want to buy your own boiler I suggest you find an installer first - this might restrict you to a very small number of Gas Safe Registered contractors indeed. Certainly would take me out of the picture.
Back to top
 Alert Moderators
johnjohnscg

from United Kingdom

Joined: 03 Jun 2011
Posts: 8
Location: London,
United Kingdom

PostPosted: Sun Jun 05, 2011 9:41 am Reply with quote

What should happen when a gassafe installer hasn't done the calcs as requested for a new install, then the customer's done their own and found the pipe to be undersized after installatio . Who's out of pocket for the upgrade pipe materials?
Back to top
 Alert Moderators
picasso

from United Kingdom

Joined: 08 Apr 2008
Posts: 5725
Location: Essex,
United Kingdom
Thanked: 1189 times

PostPosted: Sun Jun 05, 2011 9:57 am Reply with quote

johnjohnscg wrote:
What should happen when a gassafe installer hasn't done the calcs as requested for a new install, then the customer's done their own and found the pipe to be undersized after installatio . Who's out of pocket for the upgrade pipe materials?


the installer will end up out of pocket, its the installers responability to ensure its done properly,you cannot blame the customer for not doing your job the way it should be done.
Back to top
The following user says thank you to picasso for this useful post:
johnjohnscg (5 Jun 2011)
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
New Boiler installation central heating ugrade 10 840 Thu Sep 27, 2007 11:50 am
Veissman Vitodens 100 W 35kw Combi boiler gas connections 13 160 Mon Aug 29, 2011 5:57 pm
Plumber specced 30KW system boiler, online calc says 35KW 18 4420 Thu May 27, 2010 11:13 am
Should I buy Viessmann Vitodens 200 35kw combi boiler? 14 36300 Wed Nov 11, 2009 2:25 pm
(unspecified) Viessmann 35kw combi fault 3 180 Mon Dec 06, 2010 10:18 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.